Old 04-12-2014, 11:17 AM  
VikingsFan
Junior Member
registry_dropdown_33362_103319
 
Join Date: Apr 2014
Posts: 4
Default

Quote:
Originally Posted by speedy petey View Post
. . . you CANNOT use a GFI or AFCI feeder breaker in cases like this. You'll have to protect everything from the sub-panel location or local devices.
Makes total sense. I am looking to hook up a control panel for some power equipment that can be run wet. I can easily add a DIN mount AFCI to that panel, however, which should suit my purposes fine.

I'm still not clear on the whole ground / neutral bonded vs. not bonded, but the consensus seems to be that they should be connected in this scenario. I would love to simply add a ground to the run from the main building to the outbuilding, but that would be a challenge. There's no pull string and its a buried run of Sealtite that seems to make a few sharp turns.

Anyway, I appreciate all the feedback. I'm just trying to be safe here, and I'm glad there's a place I can get some solid advice.

Thanks for all the great replies!


VikingsFan is offline  
 
Reply With Quote
Old 04-12-2014, 01:24 PM  
Wuzzat?
Banned
registry_dropdown_17632_103321
 
Join Date: Jan 2010
Posts: 2,328
Liked 168 Times on 155 Posts
Likes Given: 94

Default

Quote:
Originally Posted by VikingsFan View Post
I'm still not clear on the whole ground / neutral bonded vs. not bonded,
That makes two of us.

I will add that

if
you have a neutral conductor that is sensed by a GFCI and
has a ground rod at each end,

then
the soil will be pushing current through the neutral and
this may fool the GFCI because
the current going out the hot lead is almost certain to be not the same as that returning on the neutral lead.

Having just waded through the instructions for my income tax, you may notice that the electrical code is similar. They are a bunch of IF-THEN-ELSE statements but are not quite so clearly stated.

Also, there are logical fallacies in the elec. code, probably because the people who wrote it are likely not trained in symbolic logic. Some percentage of electricians get tripped up on these fallacies.

If you haven't read
http://www.goodreads.com/book/show/6...save-your-life
on symbolic logic or done programming and you want to understand these opaque and arcane documents, I'll pray for you.
The burden for understanding is on the reader and it might be an undue burden. I'm sure this is true for the US Tax Code, and there is at least one CPA who agrees with me.

Last edited by Wuzzat?; 04-12-2014 at 02:55 PM.
Wuzzat? is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Open Ground david542 Electrical and Wiring 12 03-07-2012 11:20 AM
How to remove wood framed window bonded by liquid nail? MNYShum Windows and Doors 6 05-23-2011 10:09 AM
Neutral and Ground on a Sub-Panel wblandry Electrical and Wiring 6 06-26-2009 10:48 PM
No Ground? bnj19 Electrical and Wiring 3 02-21-2009 09:37 PM
Neutral vs Ground gfw Electrical and Wiring 3 05-15-2008 05:34 PM

Newest Threads

LATEST SPONSOR DEALS