Default Cement or plastic pad for Condensor

I am in the process of getting a condenser installed, the HVAC guy recommended a pre-cast plastic pad for the condenser to sit on.

I would rather use a concrete slab than a plastic pad, some friends told me that had issues where the pad moved, bent, collected water, etc...

My question is, which is the preferred method? If concrete is preferred, how big of a base should I make? 4'x4'? How far from the house should it be located? Thanks


drewdin is offline  
 
Reply With Quote
Old 05-19-2014, 08:56 AM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,502
Liked 511 Times on 390 Posts
Likes Given: 209

Default

Have seen both. Plastic is light weight, easier to move. But, the edges or corners get brittle and can chip. You can pour your own pad or get a precast ... I prefer poured because you can get a perfectly level base that will never move. Size it 6" larger than the equipment footprint all around.


AC.jpg  
CallMeVilla is offline  
 
Reply With Quote
Old 05-19-2014, 11:12 AM  
drewdin
Junior Member
Join Date: Aug 2012
Posts: 420
Liked 33 Times on 29 Posts
Likes Given: 99

Default

Thanks, how far from the house should i keep it? is 18" enough or does it depend on the size of the unit? Thanks
drewdin is offline  
 
Reply With Quote
Old 05-19-2014, 11:33 AM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,502
Liked 511 Times on 390 Posts
Likes Given: 209

Default

The proximity is more for servicing than anything. The 18" gap is a workable minimum. Putting it closer makes future servicing a pain.

Getting ready for the hot Summer?
CallMeVilla is offline  
 
Reply With Quote
Old 05-20-2014, 05:33 AM  
drewdin
Junior Member
Join Date: Aug 2012
Posts: 420
Liked 33 Times on 29 Posts
Likes Given: 99

Default

I am, its been muggy here and the only thing I have left to get the AC going is to install the condenser. The area where i plan on putting the condenser is on a corner of the house just like the picture above. I might just fill the whole corner with cement and not just a 4' square, so just 2" thick with some gravel underneath will be sufficient?

Thanks again
drewdin is offline  
 
Reply With Quote
Old 05-20-2014, 09:14 AM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,502
Liked 511 Times on 390 Posts
Likes Given: 209

Default

Form up with 2x4s, so you will get 3.5" ... pre-level the area with light shovel work to minimize ground disruption. Use RediCrete which has gravel in it and you will be fine ... a gravel bed is an added bonus. Just do your best to get the forms level. (Unlike the pic below) I have heard debates that the condenser MUST be perfectly level versus "Aw, BS, it can be anything close to level." I prefer the former because the unit lubricates best when level.

Another note ... set up your condensate drain so it does not undermine the pad. It can wash out and the unit will start to sink right where the condensate line drips off. Run the line away from the pad a bit.
Compressor1.jpg  
CallMeVilla is offline  
mudmixer Likes This 
Reply With Quote
Old 05-20-2014, 05:13 PM  
nealtw
Contractor
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,533
Liked 1354 Times on 1195 Posts
Likes Given: 2335

Default

I would go with a little slope maybe 1/8 per foot away from the house and shim the unit level and give it a broom finish.
nealtw is offline  
2
People Like This 
Reply With Quote
Old 05-21-2014, 06:12 PM  
daltonbrain
Junior Member
Join Date: May 2014
Posts: 7
Liked 4 Times on 3 Posts
Likes Given: 1

Default

Quote:
Originally Posted by nealtw View Post
I would go with a little slope maybe 1/8 per foot away from the house and shim the unit level and give it a broom finish.
nealtw makes a good point, add a slope to keep water from sitting on the pad.


__________________
www.dverter.com
Prevent and stop leaks in horizontal vinyl siding caused by j-channels used around windows, doors, and other wall openings.
daltonbrain is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Repair deteriorating cement on exterior cement foundation Handysyl General Home Improvement Discussion 9 10-01-2013 01:19 PM
my condensor won't shut off jimtone HVAC 2 07-15-2013 04:47 PM
Is this Condensor Fan Motor bad? mqshaw HVAC 3 05-04-2013 06:06 AM
Help replacing a condensor motor. Bryan330 HVAC 2 03-31-2010 02:00 PM
Lennox Condensor BWonsch HVAC 1 07-01-2009 10:29 AM

Newest Threads

LATEST SPONSOR DEALS