Hello all,

We just moved into a new house and the previous owner ran two 20amp circuits with 15 amp receptacles in the garage via conduit. There are four wires, red, black, white, green shared between the two circuits. He shared the neutral between the two circuits. Is this safe? Legal? Can a ground be shared between two(or more) circuits?

I want to add another circuit to the garage as well (20amp). If multiple circuits can share a neutral, is it limited to two?

The red is stripped in a couple junction boxes so I'll be pulling new wire for that one as well. (I found these as the receptacles were not tight and I pulled them out to figure out why.)

Thank you!


blueskyhighpilot is offline  
 
Reply With Quote
Old 05-29-2014, 11:31 AM  
bud16415
Fixer Upper
HRT_ADMIN.png
 
bud16415's Avatar
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 4,260
Liked 1415 Times on 1082 Posts
Likes Given: 765

Default

It’s somewhat common to do that and to code. The idea is I believe the red and black are from opposite legs of the 220 and are out of phase so when one is conducting the other is down. That way the white common is only seeing the current of one at a time. It’s called a multi wire branch circuit.


link

http://ecmweb.com/code-basics/branch-circuits-part-one

http://www.jadelearning.com/thejunct...its-nec-210-4/



Last edited by bud16415; 05-29-2014 at 11:46 AM.
bud16415 is offline  
 
Reply With Quote
Old 05-29-2014, 12:22 PM  
kok328
Senior Member
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,718
Liked 241 Times on 204 Posts
Likes Given: 111

Default

Might want to change those outlets to 20 Amp instead of 15 Amp.
What gauge wire was run for these outlets?
kok328 is offline  
 
Reply With Quote
Old 05-29-2014, 12:45 PM  
blueskyhighpilot
Junior Member
Join Date: May 2014
Posts: 3
Default

Thank you!
blueskyhighpilot is offline  
 
Reply With Quote
Old 05-29-2014, 12:46 PM  
blueskyhighpilot
Junior Member
Join Date: May 2014
Posts: 3
Default

Quote:
Originally Posted by kok328 View Post
Might want to change those outlets to 20 Amp instead of 15 Amp.
What gauge wire was run for these outlets?

Solid 12 awg. I was thinking of changing them to 20amp outlets.
blueskyhighpilot is offline  
 
Reply With Quote
Old 05-29-2014, 03:30 PM  
kok328
Senior Member
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,718
Liked 241 Times on 204 Posts
Likes Given: 111

Default

Solid core in conduit doesn't sound right.
Could be a local code thing but, I can't imagine what wire was used in conduit that is solid core w/o being romex or MC.
In which case, you need to get some more feedback on the type of wire used and it's compliance in this application.
kok328 is offline  
 
Reply With Quote
Old 09-06-2014, 04:10 AM  
WyrTwister
Senior Member
Join Date: May 2014
Posts: 136
Liked 15 Times on 14 Posts

Default

Very common , if the red and black are on opposite phases . The white / neutral only carries the unbalance load between the 2 " hots " .

On 120 / 240 VAC single phase service .

Best I remember multiple 15 amp receptacles are legal on a 20 amp circuit .

Pretty much an unlimited number of " hots " can share a green / earth ground . As long as the green has equal to or higher ampacity than any individual " hots " .

Adding another circuit would involve additional " hots " and neutrals . That can share the same green / earth ground .

God bless
Wyr
WyrTwister is offline  
 
Reply With Quote
Old 09-06-2014, 05:24 AM  
speedy petey
Lic.Electrical Contractor
Join Date: Mar 2006
Posts: 470
Liked 44 Times on 31 Posts
Likes Given: 25

Default

OK, I know this thread is from several months ago, and the OP hasn't been back here since June, but I'd like to clear a few things up.

-No reason to change the receptacles to 20A as suggested, unless of course they are needed for a tool or larger appliance, which is unlikely. As long as there is more than just one simplex receptacle on the 20A circuit 15A are fine. And depending on the grade/quality there is absolutely NO difference other than the prong configuration. ALL 15A duplex receptacles are rated for 20A feed-thru, even the cheap $.59 ones.

-It was also suggested that solid wire was somehow strange or not acceptable. This is very misleading. Solid wire is absolutely typical and perfectly acceptable. Solid THHN is no different than stranded in application.
speedy petey is offline  
2
People Like This 
Reply With Quote
Old 09-06-2014, 10:41 AM  
WyrTwister
Senior Member
Join Date: May 2014
Posts: 136
Liked 15 Times on 14 Posts

Default

I agree , we use solid # 12 THHN all the time . Easier to bend around and put under screws for receptacles or switches .

" Back - stab " wired devices were a very bad idea . I am pretty sure they are no longer made ( thankfully ) .

At one time , around here , a 200 amp meter base was the " max " . We now can use up to about a 320 amp meter base . Maybe up to close to 400 amps ?

But traditionally 200 amps is sufficient for a small to medium size home , even if all electric , except in the coldest climates . This does not include the use of instanious / tankless whole house water heaters . Which I have no experience with .

God bless
Wyr


WyrTwister is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Two Hots -- One Box GeorgyD Electrical and Wiring 6 07-04-2013 02:01 PM
Two Circuits Sharing Junction Box doechsli Electrical and Wiring 4 04-03-2013 07:26 PM
Sharing white neutral wires Nestor_Kelebay Electrical and Wiring 2 08-28-2009 10:48 PM



Newest Threads