Default Venting problem.

I recently moved my water heater to a more central location in the basement to try and get hot water to all places faster. It is now located next to the furnace in the basement (they share the same flue).

Now, when I turn on the furnace, I get a slight flue gas odor in the basement like the flue is not drawing. This never happened before, even when it was just the furnace using that vent flue.

One other thing changed. When we had the roof redone last year, the roofers lost the rain cap on the furnace vent flue. They replaced it with a different unit that looks to have slots on the side of a round cap rather than the bigger openings on the old unit.

Is it possible that this new flue rain cap is more restrictive than the original one?



__________________

Hack (a.k.a. Jeff)

Hack is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2007, 12:17 PM  
travelover
Senior Member
 
Join Date: Aug 2007
Posts: 693
Liked 2 Times on 2 Posts

Default

Could you take the flue cap off temporarily for a test?

Also you could keep a carbon monixide detector in the area to see if there is CO being dispersed into the basement.



__________________
travelover is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2007, 01:16 PM  
Hack
Senior Member
 
Hack's Avatar
 
Join Date: Nov 2007
Location: Petaluma, CA
Posts: 194
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by travelover View Post
Could you take the flue cap off temporarily for a test?

Also you could keep a carbon monixide detector in the area to see if there is CO being dispersed into the basement.
Great idea...Thanks! I can take it off for a test, but I think I need a taller ladder. Mine is only 25'
__________________

Hack (a.k.a. Jeff)

Hack is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2007, 03:14 PM  
travelover
Senior Member
 
Join Date: Aug 2007
Posts: 693
Liked 2 Times on 2 Posts

Default

Quote:
Originally Posted by Hack View Post
Great idea...Thanks! I can take it off for a test, but I think I need a taller ladder. Mine is only 25'
You can rent ladders - I think even Home Depot rents 'em.
__________________
travelover is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2007, 06:34 PM  
glennjanie
Senior Member
 
Join Date: Mar 2006
Posts: 2,990
Liked 2 Times on 2 Posts

Send a message via AIM to glennjanie
Default

Hey Jeff:
The American Gas Association has a sizing chart for gas vents (or you can go to Hart and Cooley to get one). Was it always a shared vent? If it was not the backflow indicates that the furnace vent is too small to carry the water heater vent too.
If you feel that the cap is restricting the flow you can still get the one that looks like the Chinaman's hat.
Glenn

__________________
glennjanie is offline  
 
Reply With Quote Quick reply to this message
Old 11-15-2007, 12:06 PM  
Hack
Senior Member
 
Hack's Avatar
 
Join Date: Nov 2007
Location: Petaluma, CA
Posts: 194
Liked 1 Times on 1 Posts

Default

Thanks for the resources.

I tend to believe that it is the vent cap because even when one of the two is running, I have this problem (which I didn't have before).

I'm heading out to get a Chinaman's Hat type vent today and swap it out. Only one problem...I think I need to know the PC term for that cap here in CA . I might get called out by the ACLU otherwise

__________________

Hack (a.k.a. Jeff)

Hack is offline  
 
Reply With Quote Quick reply to this message
Old 11-15-2007, 12:39 PM  
travelover
Senior Member
 
Join Date: Aug 2007
Posts: 693
Liked 2 Times on 2 Posts

Default

Quote:
Originally Posted by Hack View Post
Thanks for the resources.

I tend to believe that it is the vent cap because even when one of the two is running, I have this problem (which I didn't have before).

I'm heading out to get a Chinaman's Hat type vent today and swap it out. Only one problem...I think I need to know the PC term for that cap here in CA . I might get called out by the ACLU otherwise

Just ask to see the chimney caps, then point out the one you need.
__________________
travelover is offline  
 
Reply With Quote Quick reply to this message
Old 11-26-2007, 11:05 AM  
Hack
Senior Member
 
Hack's Avatar
 
Join Date: Nov 2007
Location: Petaluma, CA
Posts: 194
Liked 1 Times on 1 Posts

Default

O.K. It worked. I purchased a "high wind" rain cap which has quite a bit more opening around the sides. I got the high wind version because we do have quite a bit of wind.

After it was installed, no more smell

I also bought, and still plan to install vents up high on the basement wall as well. Installation guidelines say to do this, but I just hadn't done it yet...

__________________

Hack (a.k.a. Jeff)

Hack is offline  
 
Reply With Quote Quick reply to this message
Old 11-26-2007, 12:46 PM  
travelover
Senior Member
 
Join Date: Aug 2007
Posts: 693
Liked 2 Times on 2 Posts

Default

Thanks for reporting back. Your experience will help others.

And congratulations for sticking with it until you solved the problem.

__________________
travelover is offline  
 
Reply With Quote Quick reply to this message
Old 12-17-2007, 11:24 AM  
Hack
Senior Member
 
Hack's Avatar
 
Join Date: Nov 2007
Location: Petaluma, CA
Posts: 194
Liked 1 Times on 1 Posts

Default

Well, I was a bit early with my celebration of success. When I went down to the basement the next day to do some work, it smelled in the basement. I could also detect the smell in the house just a bit...

So, back to the hardware store to get some more parts and change the layout of the venting to better the flow path of the flue gases.

Below are the before and after layouts of the vent piping. Before, there was a "TEE" where the water heater tapped into the flue from the furnace. When the water heater was on, flue gases would get to the "tee" and go both directions.

Now, I've re-routed both to a "TEE" up higher. This prevents backdraft of flue gases.

So far, so good



layout.jpg   layout 2.jpg  
__________________

Hack (a.k.a. Jeff)

Hack is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
High limit problem on Trane XE90 Garvey HVAC 1 11-10-2011 09:33 AM
Intermittent Problem with Decorative Low Voltage Fixture mman Electrical and Wiring 2 11-07-2008 07:00 AM
GFCI breaker problem a4rye Electrical and Wiring 3 09-26-2008 09:37 AM
Stymied by window leakage problem. Matth3w Windows and Doors 10 06-09-2008 08:15 AM
Dryer Venting GolfnRL General Appliance Discussion 3 04-09-2008 08:20 AM

Newest Threads

LATEST SPONSOR DEALS