Default Gas Line Tests - HELP!

My contractor put in a gas line for a cooktop and used tracpipe so there wouldn't be any unions,etc in finished ceiling.

He tested the line with 5lbs of pressure for 24 hrs. It dropped about 3/4 lb. He was ok with that saying the air cools, etc and the line doesn't have to support 5 anyway, that's just so they can spray the blue magic solution on the joints, etc. He said his test gauge is old and might have a very small leak too. He said to make me feel better he'd drop it to 2lb and do 24 hr. It dropped about 1/2+lb still in last 24 hrs.

His explanation is that there is no leak, the gas company would test 1lb for 20 minutes and call it good. He's an engineer, and has 25 yrs in the business as a certified hvac, restaurant eq guy.

Is there a legitimate reason for it to lose 25% of the pressure? Should I let him turn it on?



__________________

Last edited by markg; 11-21-2007 at 10:13 AM.
markg is offline  
 
Reply With Quote Quick reply to this message
Old 11-21-2007, 10:45 AM  
glennjanie
Senior Member
 
Join Date: Mar 2006
Posts: 2,990
Liked 2 Times on 2 Posts

Send a message via AIM to glennjanie
Default

Welcome MarkG:
The change in temperature will certainly change the pressure. If you had a leak in the line the air would drop to 0 in 5 to 10 minutes. He is also correct about the gas pressure; it will only be 6oz. which is not much more than a baby's breath.
He has done a good job for you; pay the man and enjoy your new gas stove.
Glenn



__________________
glennjanie is offline  
 
Reply With Quote Quick reply to this message
Old 06-14-2008, 08:15 PM  
geo fan
Junior Member
 
Join Date: Jun 2008
Posts: 6
Default you have a leak

what he should do is get him to put at least 30 psi of nitogen which wont condense and spray soap bubbles on every joint in the system I have seen the tracpipe adapters leak if the cut wasnt clean if he keeps blowing you off give a call to the town hall the the inspector has a heads up on the situation in CT they want a 30 psi test to hold for 24 hours


oil spills and gas kills

__________________
geo fan is offline  
 
Reply With Quote Quick reply to this message
Old 06-15-2008, 12:35 PM  
majakdragon
Senior Member
 
Join Date: Sep 2006
Location: Lafe Arkansas, Arkansas
Posts: 165
Default

Only "real" problem I would have with this contractor is his excuse about the "old gauge". I feel that if you are using equipment to test for leaks, you should at least have decent equipment. Hopefully the gas company will be testing this line before it is turned on.

__________________

if you have never made a mistake, you probably haven't done much.

majakdragon is offline  
 
Reply With Quote Quick reply to this message
Old 08-05-2008, 09:29 AM  
frodo
Senior Member
 
Join Date: Aug 2008
Posts: 316
Liked 74 Times on 59 Posts
Likes Given: 58

Default leak

if a system is holding pressure,it will not drop pressure. true that ambient
can effect a gauge, by 1 or 2 lbs. if the gauge has droped, ther is a slow leak. it does not make a tinkers damn. that ''just'' low pressure will be delivered thru the pipe. a leak is a leak. if it is a low pressure system, then you will have gas pooling up in a traped space. awaiting a source of ignition.
or it could be venting out into the atmosphere. tell him that you want to see a ''new'' gauge on the pipe. and that you will not accept a drop in pressure. the best gauge for him to use, would be a mercury gauge.
they let you know right now if ther is a leak.

__________________
frodo is offline  
 
Reply With Quote Quick reply to this message
Old 05-10-2009, 12:47 AM  
Ace28
Junior Member
 
Join Date: May 2009
Posts: 2
Default

Quote:
Originally Posted by majakdragon View Post
Only "real" problem I would have with this contractor is his excuse about the "old gauge". I feel that if you are using equipment to test for leaks, you should at least have decent equipment. Hopefully the gas company will be testing this line before it is turned on.
I agree, anytime I have a leak the 1st place I always check is the gauge/test setup.
__________________
Ace28 is offline  
 
Reply With Quote Quick reply to this message
Old 05-10-2009, 08:57 AM  
MACPLUMB
35 YEAR MASTER PLUMBER
 
Join Date: Apr 2009
Location: NORTH HOUSTON, TEXAS, T E X A S
Posts: 19
Default Gas line test ! ! !

FIRST OF ALL THE GAS CO. DOE'S NOT TEST THE GAS PIPE ! !

THAT IS WHY YOU USE A LIC. PLUMBER AND PAY FOR THE PERMIT,

THE GAS CO. GO'ES BY THE INSPECTORS SIGN OFF AS JOB COMPLETE

NO NO YOU SHOULD NOT ACCEPT THIS AMOUNT OF LEAK AS NO BIG DEAL

GOOGLE GAS EXPLOSIONS ON INTERNET TO SEE WHAT I MEAN ! !

I GET GOOGLE ALERTS EVERYDAY ON GAS EXPLOSIONS SOMEWHERE CHECK

YOUR NEWS FOR LAST WEEK WHERE A STRIP MALL WAS DESTROYED

BY A GAS LEAK THEY CAUGHT THIS ONE ON VIDEO WITH THE FIRE DEPT.

STANDING BY WHILE IT WAS BEING WORKED ON ! !

ONLY ACCEPT THE SIGNOFF BY A LIC. INSPECTOR YOUR FAMILY IS TOO
PRECIOUS TO TAKE A CHANCE ON ANY THING LESS ! !

__________________

MACPLUMB
E-MAIL [email]JERRYMAC@UTAHWEB.COM[/email]
35 YRS. MASTER PLUMBER
WITH A PH.D. IN WATER HEATEROLGY

MACPLUMB is offline  
 
Reply With Quote Quick reply to this message
Old 05-11-2009, 12:09 AM  
Redwood
Certified Lunatic
 
Redwood's Avatar
 
Join Date: Apr 2009
Location: Olde Tyme, Connecticut
Posts: 887
Default

Quote:
Originally Posted by geo fan View Post
what he should do is get him to put at least 30 psi of nitogen which wont condense and spray soap bubbles on every joint in the system I have seen the tracpipe adapters leak if the cut wasnt clean if he keeps blowing you off give a call to the town hall the the inspector has a heads up on the situation in CT they want a 30 psi test to hold for 24 hours


oil spills and gas kills
CSST is not to be tested with soap solution!
It can cause corrosion of the CSST!


__________________
Redwood is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
sewer line has roots backflow??? papason Plumbing Forum 6 09-20-2009 11:55 AM
Well Line Ruptured? Josie Plumbing Forum 6 04-20-2008 11:34 PM
New Sewer Line Kerrylib Plumbing Forum 4 05-12-2007 10:27 PM
Water Supply Line and Building Code Carcosa Plumbing Forum 3 01-20-2007 11:18 AM
fuel line to furnace bethany14 HVAC 5 11-21-2006 07:35 AM

Newest Threads

LATEST SPONSOR DEALS