Old 02-05-2008, 11:00 AM  
LanceM
Junior Member
 
Join Date: Feb 2008
Posts: 8
Default Working Around Furring Strips

Hello, new to the group here. I'm just starting to renovate our basement and have a question as to the best way to work outlet wiring around the furring strips.

The furring strips will be 2x3's covered with 1/2" drywall. The room will have a suspended ceiling. Wiring will be simple and consist of a few outlets. What is the best way to run the outlet wiring and work it around the furring strips? A) Should I drop a line down vertically from the ceiling between the furring strips to the outlet or B) Somehow drill holes in the sides of the 2x3's and feed the wire through that way? Thanks in advance.
Lance



__________________
LanceM is offline  
 
Reply With Quote Quick reply to this message
Old 02-05-2008, 11:11 AM  
Daryl in Nanoose
Senior Member
 
Daryl in Nanoose's Avatar
 
Join Date: Feb 2006
Location: Nanoose Bay, BC
Posts: 762
Liked 3 Times on 3 Posts
Likes Given: 5

Default

If your running 2x3's like a stardard wall ( 2-1/2" away from exterior wall) keep your holes towards the back of the 2x3. If your running the 2x3's on flat ( 1-1/2" away from exreior wall) then go up and down between the 2x3's, there just is not enough room for wire on 1-1/2" safely unless your willing to put metal plates directly in front of where the wire were run.



__________________

[url]http://edhome.shawwebspace.ca/[/url]

Daryl in Nanoose is offline  
 
Reply With Quote Quick reply to this message
Old 02-05-2008, 03:16 PM  
LanceM
Junior Member
 
Join Date: Feb 2008
Posts: 8
Default Working Around Furring Strips

Quote:
Originally Posted by Daryl in Nanoose View Post
If your running 2x3's like a stardard wall ( 2-1/2" away from exterior wall) keep your holes towards the back of the 2x3. If your running the 2x3's on flat ( 1-1/2" away from exreior wall) then go up and down between the 2x3's, there just is not enough room for wire on 1-1/2" safely unless your willing to put metal plates directly in front of where the wire were run.
Yes, they're laying flat. I'll come down from the top. Thanks!
__________________
LanceM is offline  
 
Reply With Quote Quick reply to this message
Old 02-05-2008, 10:38 PM  
Daryl in Nanoose
Senior Member
 
Daryl in Nanoose's Avatar
 
Join Date: Feb 2006
Location: Nanoose Bay, BC
Posts: 762
Liked 3 Times on 3 Posts
Likes Given: 5

Default

Your welcome, let us know with pics if possible how it all turns out for you.

__________________

[url]http://edhome.shawwebspace.ca/[/url]

Daryl in Nanoose is offline  
 
Reply With Quote Quick reply to this message
Old 02-10-2008, 12:51 PM  
pressureseal
Junior Member
 
Join Date: Jan 2008
Posts: 18
Default

Hi. I have the same issue with installing electrical around furring strips and I just wanted to make sure I understand how this works. I am working around 2 " x 2" strips, this is the original framing in my basement and I would like to avoid re-framing. I am planning to put drywall up over top.

From your post, it sounded like I can run the wires in between the strips and I don't have to install metal plates in that case. Is that correct? Also, when you say, install between the strips, do you mean right in the middle or would you anchor to the side of a furring strip?

__________________
pressureseal is offline  
 
Reply With Quote Quick reply to this message
Old 02-10-2008, 10:23 PM  
Daryl in Nanoose
Senior Member
 
Daryl in Nanoose's Avatar
 
Join Date: Feb 2006
Location: Nanoose Bay, BC
Posts: 762
Liked 3 Times on 3 Posts
Likes Given: 5

Default

You treat it like it was a stud. Staple it to the sides. The theory is that if some one finds a stud and puts a screw or nail it won't penetrate the wire.

__________________

[url]http://edhome.shawwebspace.ca/[/url]

Daryl in Nanoose is offline  
 
Reply With Quote Quick reply to this message
Old 02-11-2008, 07:04 PM  
pressureseal
Junior Member
 
Join Date: Jan 2008
Posts: 18
Default

Ok. If I staple the wiring to the sides of the 2x2's, then in that case do I need to use metal plates over top or is that ONLY where they go through the wood.

__________________
pressureseal is offline  
 
Reply With Quote Quick reply to this message
Old 02-11-2008, 09:11 PM  
Daryl in Nanoose
Senior Member
 
Daryl in Nanoose's Avatar
 
Join Date: Feb 2006
Location: Nanoose Bay, BC
Posts: 762
Liked 3 Times on 3 Posts
Likes Given: 5

Default

Quote:
Originally Posted by pressureseal View Post
Ok. If I staple the wiring to the sides of the 2x2's, then in that case do I need to use metal plates over top or is that ONLY where they go through the wood.
Only where they go through the wood as far as I know.
__________________

[url]http://edhome.shawwebspace.ca/[/url]

Daryl in Nanoose is offline  
 
Reply With Quote Quick reply to this message
Old 02-12-2008, 12:57 AM  
ToolGuy
Senior Member
 
ToolGuy's Avatar
 
Join Date: Nov 2007
Posts: 482
Liked 1 Times on 1 Posts

Default

The metal plate is to protect the wire from nails or screws when someone fastens into the stud, such as drywall or hanging shelves or a mirror. Thus, would only apply when running wiring through the stud.



__________________

[COLOR="DarkRed"][B]~ ToolGuy ~[/B][/COLOR]

[I]Save money on tools at [URL="http://mytoolbox.net"]MyToolbox.net[/URL]
[/I]

ToolGuy is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
furring out basement, help? mikeydiy Flooring 7 03-27-2011 11:17 AM
Garbage Disposal and dishwasher not working Kat42 Plumbing Forum 6 04-14-2009 10:55 PM
"Giant" hot water tank stoped working Xilbus Plumbing Forum 3 04-30-2008 07:48 AM
Basement Furring Strips LanceM Flooring 6 02-06-2008 08:07 PM
Fan in hallway timer in garage, stoped working Kevdog98 HVAC 1 03-23-2007 06:29 PM

Newest Threads

LATEST SPONSOR DEALS