Old 05-08-2008, 06:44 PM  
Scottphys
Junior Member
 
Join Date: May 2008
Posts: 4
Default Condenser fan won't shut off

This is a strange problem with my home AC...my condenser fan will not stop unless I kill the power to the unit.

I have replaced all of the components (contactor, capacitors, and even the fan motor) in the outside unit except the compressor. I have isolated the unit from the inside electronics by removing the wires from the thermostat to the contactor: no luck. If I take the start and run leads from the compressor out of the circuit, then the fan will stop.

I looked at the compressor connections (at the compressor) and cleaned them off...also no luck.

Am I missing something? Has anyone seen this?

Thanks for any help and ideas you all may have!

Scott



__________________
Scottphys is offline  
 
Reply With Quote Quick reply to this message
Old 05-08-2008, 08:13 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,212
Liked 114 Times on 99 Posts
Likes Given: 65

Default

Not knowing what type of setup you have (make/model), I can only speculate on a few scenarios.

= switching relay is stuck
= internal compressor relay is stuck
= bad hi pressure switch



__________________
kok328 is online now  
 
Reply With Quote Quick reply to this message
Old 05-08-2008, 09:00 PM  
Scottphys
Junior Member
 
Join Date: May 2008
Posts: 4
Default

I don't have much experience in HVAC, but it seems like a very basic system. It's a Bryant unit using a Copeland scroll compressor.

The outside unit seems very simple. The only electrical components are the contactor, cap, and motor. The only other component inside the condenser is the compressor.

I have a feeling that the compressor is the problem...

Why didn't I get into the HVAC business ????????

__________________
Scottphys is offline  
 
Reply With Quote Quick reply to this message
Old 05-08-2008, 11:40 PM  
Damon
Junior Member
 
Join Date: May 2008
Posts: 5
Default

Quote:
Originally Posted by Scottphys View Post
This is a strange problem with my home AC...my condenser fan will not stop unless I kill the power to the unit.

I have replaced all of the components (contactor, capacitors, and even the fan motor) in the outside unit except the compressor. I have isolated the unit from the inside electronics by removing the wires from the thermostat to the contactor: no luck. If I take the start and run leads from the compressor out of the circuit, then the fan will stop.

I looked at the compressor connections (at the compressor) and cleaned them off...also no luck.

Am I missing something? Has anyone seen this?

Thanks for any help and ideas you all may have!

Scott
the problem you have is a wiring issue. If the compressor not running but the fan motor is, that means the contactor is open but the fan is still energized. The hot wires to the fan motor are on the hot side of the conotactor. Connect the fan motor to the same side of the contactor as the compressor leads.

If the compressor is running with the fan motor, then the problem is with the contactor. Use a volt meter/multimeter to measure the voltage across the low voltage control wire terminals. If the thermostat is turned off, the voltage should read 0. If it doesn't, you have a low voltage wiring issue. I can help you with that over time. If the voltage is 0 but the contactor is energized, you have the wrong contactor. Replace it with a 2 pole Normally Open contactor.
__________________
Damon is offline  
 
Reply With Quote Quick reply to this message
Old 05-09-2008, 04:54 PM  
Scottphys
Junior Member
 
Join Date: May 2008
Posts: 4
Default

Quote:
Originally Posted by Damon View Post
Connect the fan motor to the same side of the contactor as the compressor leads.
It is. My DVM reads ~130 volts across the output of the contactor while the one leg of the contactor is open (the other pole is straight through). Compressor is not on, fan is.
If I remove the compressor leads from the contactor output, the fan stops. It seems as if the 130V is coming through the compressor leads! Is it possible that something (electrical) is bad inside the compressor without actually affecting the compression function?

Quote:
Originally Posted by Damon View Post
If the thermostat is turned off, the voltage should read 0.
I was worried about that. All of the testing I've done is with the thermostat leads removed from the contactor so I can isolate the outside unit.
__________________
Scottphys is offline  
 
Reply With Quote Quick reply to this message
Old 05-12-2008, 07:05 AM  
Damon
Junior Member
 
Join Date: May 2008
Posts: 5
Default Repy to 130V across contactor

QUOTE=Scottphys;18897]It is. My DVM reads ~130 volts across the output of the contactor while the one leg of the contactor is open (the other pole is straight through). Compressor is not on, fan is.
If I remove the compressor leads from the contactor output, the fan stops. It seems as if the 130V is coming through the compressor leads! Is it possible that something (electrical) is bad inside the compressor without actually affecting the compression function?

I was worried about that. All of the testing I've done is with the thermostat leads removed from the contactor so I can isolate the outside unit.[/QUOTE]

Is the fan turning at approx 1/2 speed?
What other components if any are connected to the contactor?
Electricaly, if you are measuring V across a single pole contactor with the contacts open, you should get 0V. If you measure across either lead to ground you should get approx 120-130V. Can you attach a picture of the contactor with all wires connected?

Another thought is that if the compressor has a crankcase heater for cold weather, that may be complicating the problem. If it does, disconnect those wires from the contactor and see if that solves the problem.

__________________

Last edited by Damon; 05-12-2008 at 07:09 AM.
Damon is offline  
 
Reply With Quote Quick reply to this message
Old 05-12-2008, 05:08 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,212
Liked 114 Times on 99 Posts
Likes Given: 65

Default

Change out the contactor and the switching relay. Post back if your still having issues.

__________________
kok328 is online now  
 
Reply With Quote Quick reply to this message
Old 05-18-2008, 05:21 PM  
Scottphys
Junior Member
 
Join Date: May 2008
Posts: 4
Default Resolution...

Thought I'd give a quick reply so maybe I can help someone in the future with this issue.

I had a "pro" come out and look. The compressor blew out one of its three contacts and current is feeding back through to the fan. Also, there is a small refrigerant leak near those connections.

I missed the issue with the connectors when I cleaned them originally. When I pulled the plug from the compressor, one of the leads was attached to the plug, the other two leads were attached to the compressor. I just figured this was the way the connection was "keyed"...what can I say...inexperience with compressors!

I've also noticed some strange behavior that may help someone in the future diagnose a similar problem: the condenser fan will operate normal (fan on when compressor is on, fan off when compressor is off) when no cold air comes out, but when the fan stays on (regardless of compressor), the air is cold. Maybe the start windings in the compressor is connected to the contacts that blew out??

In any case, I want to thank all of you for your help. It's extremely appreciated!

__________________
Scottphys is offline  
 
Reply With Quote Quick reply to this message
Old 07-09-2013, 09:27 PM  
jimtone
Junior Member
 
Join Date: Jul 2013
Posts: 4
Default

My system is doing the same thing, and I turned on all power and switches and set the tstat to cool and fan to auto with the temp lower to make the (air handler) furnace activate and when I switch the tstat to off from cool the furnace fan shuts off but the condenser keeps running. I opened the tstat down to the wire terminals and removed the wire from Y while all were running and the furnace fan stopped. I hooked the wire back up and went out to the condenser and pulled the fuse block and checked to find the contactor was still drawn down and when I went inside to turn off the tstat and checked the contactor had released which told me it was not welded together at the contacts. I also turned everything back on and removed one of the low voltage wires from the contactor and the condenser shut off and came back on when the wire was replaced to the contactor. I'm thinking/guessing that the tstat is bad or that the wires leading from it to the furnace have a short?? This is a single speed York condenser hooked to a Rheem verticle air handler with a mechanical tstat without mercury in glass tube. I've cleaned the contacts on the tstat but no change. The low voltage wires leading to the furnace are only 7 feet long so I think I'll just get a new length and swap it out tomorrow before buying a new thermostat?



__________________
jimtone is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
GE Profile refrigerator condenser fan not turning on Quattro HVAC 18 08-31-2012 08:22 AM
Condenser fan motor Tonnyray HVAC 1 09-10-2007 11:06 AM
fan wont shut off gbliss HVAC 2 04-16-2007 10:06 AM
tub wont shut off mikeblo17 General Home Improvement Discussion 2 07-06-2006 09:41 AM
blower fan won't shut off popgun2k HVAC 1 12-05-2005 08:30 PM