Default Pressure Testing Black Pipe

Hi, I recently had a new run of black pipe installed from the meter to where the new boiler will be installed. They pressure tested the line to 25psi and 5 days later it dropped to 5psi and failed inspection. The plumber returned, pressurized the line to 100psi and found a leak at a joint. The joint was fixed and the line was pressurized again to 26psi. 6 days later, today actually, the gauge now reads 14 psi. The re-inspection is scheduled for this coming Wed. but it looks like it may fail again.

Is there a certain amount of time or a minimum amount of pressure that the pipe has to hold indefinitely?

Thanks
John



__________________
jmol is offline  
 
Reply With Quote Quick reply to this message
Old 11-04-2008, 03:20 PM  
glennjanie
Senior Member
 
Join Date: Mar 2006
Posts: 2,990
Liked 2 Times on 2 Posts

Send a message via AIM to glennjanie
Default

Welcome John:
If there is a leak, it will loose 100 pounds in hours; if there is not a leak, it will hold 25 pounds forever. I personally like to use 15 pounds and soap spray the joints; if there is a leak the soap will bubble right away.
If the pipe is exposed to weather changes, the pressure can vary 5 to 10 pounds either way so, I don't like long holding periods. It sounds like your installer is very concientious and I think you will be fine.
Glenn



__________________
glennjanie is offline  
 
Reply With Quote Quick reply to this message
Old 11-04-2008, 11:26 PM  
triple D
Senior Member
 
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default in our area....

The pressure must be at 15psi. any more or less and you fail. I have never seen fluxuation in pressure that was really noticible (more than 1psi.) and I have watched many guages over the years. Some I have seen on test for weeks at a time with no change at all. So like glenn says, go for 15psi, and then wait a couple days. If it leaks down, you do have a leak. Good luck.....

__________________

[COLOR="DarkGreen"][FONT="Franklin Gothic Medium"]See my work-Check out my album. "Git 'Er Done":D [/FONT][/COLOR]

triple D is offline  
 
Reply With Quote Quick reply to this message
Old 11-05-2008, 10:37 AM  
jmol
Junior Member
 
Join Date: Nov 2008
Posts: 2
Default

Thanks for the info guys, the new boiler is being installed as I type this reply. Yesterday, the plumber came back and we found two slight air bubbles at two separate elbows. They fixed the leaks, repressurized to 30psi and it held 30psi for 24hrs. The reinspection was earlier today and it passed.

Thanks again
John

__________________

Last edited by jmol; 11-05-2008 at 11:34 AM.
jmol is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Black pipe for water maverick Plumbing Forum 6 05-01-2013 03:50 PM
Pressure balanced faucets for the shower, yes or no? davefoc Plumbing Forum 5 04-13-2009 07:54 PM
Pressure testing a gas line for min and max PSI groga01 Plumbing Forum 3 01-31-2008 10:03 PM
stove - 50 amp White Red Black Black Conduit - 3 hot? where's green? sholleran Electrical and Wiring 9 01-30-2008 12:58 AM
Furnace draft pressure too low Alwaysfixinsumthin HVAC 1 10-27-2007 12:18 AM

Newest Threads

LATEST SPONSOR DEALS