Default What is the fuel type, gas or oil

What is your fuel type: gas or oil. If you have gas, your ignitor would be your problem. Look into the glass in front of the burners. My igniter is on the left side. If the igniter does not glow cherry red, the whole igniter, the temperature sensor will not open the gas valve. Look at the control module flashing light. This tell you what the cause of the failure, quite simple. Go the the York web page and download the manual for your furnas. A new ignitor locally $60, web best $30. Keep a new one just in case. I was impatient at midnight, so I used my propane torch instead of the ignighter to light the furnas. Kids get cranky at 50 degrees in there PJs.


Chopsaw2843 is offline  
 
Reply With Quote
Old 01-06-2011, 09:02 PM  
Dtodd
Junior Member
Join Date: Dec 2010
Location: Highland, IL
Posts: 6
Default

It's a 40VA transformer.
With the vent blower off I was getting 26.5 volts out, vent blower on
24.6 volts out and 24.1 volts back from thermostat.
I got this after I took the120 power on/off switch out & wire direct.
Voltage at the circuit breaker was 118.8 and at fan limit switch 118.2 - a drastic improvement over 94.4 with the on/off switched wired in line.
The vent fan which is rated at .7a is now reading .54a versus .65a.
Your thoughts?
Thanks again!
Dave


Dtodd is offline  
 
Reply With Quote
Old 01-06-2011, 09:25 PM  
paul52446m
Senior Member
Join Date: Oct 2010
Location: Houghton Lake, Mi.
Posts: 435
Liked 1 Times on 1 Posts

Default

The 24volt system should work ok as long as you don't drop any lower.
When you say vent blower, are you talking main blower or stack inducer fan?
you should not be dropping 2 volts by running one relay to start a blower. Later paul
paul52446m is offline  
 
Reply With Quote
Old 01-07-2011, 08:24 PM  
Dtodd
Junior Member
Join Date: Dec 2010
Location: Highland, IL
Posts: 6
Default

Paul
It was the stack inducer fan.
Installed new on/off power switch tonight.
With both fans running now getting 24.7v @ transformer, 24.2v back from thermostat and 24.0v @ fan limit switch and 119.2v on line load @ fan limit switch.
Hasn't miss-fired yet. Thanks to your help I think the problem is solved!
If I have future problem I will try changing out and upping the Va of the transformer
Thank you so very much for your help!
Dave
Dtodd is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
York Stellar Plus flame won't say lit for more than a second frank_mccormick HVAC 4 01-24-2013 10:24 PM
New Coleman/York furnace blower erratic Quattro HVAC 8 11-29-2012 09:12 PM
York Stellar Plus won't always ignite PFW HVAC 0 01-26-2012 03:59 PM
York stellar plus keeps shutting down djh860 HVAC 6 01-05-2010 05:26 AM
York Stellar Plus won’t ignite rodge HVAC 24 01-11-2009 05:36 AM



Newest Threads