Default Furnace Advice Needed

Hello to all,
Just wanted to see if I can get some helpful advice from someone who knows about furnaces before I called someone in to fix it, maybe my problem isn't too bad and I can fix it myself!

My furnace seems to be having some problems, here is a brief description of what his happening.

The furnace appears to be working and heating but after about 3-5hrs, it will just quit. So at first, I would turn up the thermastat as high as it goes to see if the furnace would kick in, it wouldn't, but then when i turn it "on" to the fan, it works. Then i went to the furnace itself and opened up the unit (after turning off the power) and made sure all the wires, etc were good, it appears there were no loose wires and the one fuse appeared to be in good shape, I also changed the furnace filter at the same time. for me to get the furnace working again, I have to flip off and on the breaker switch, the furnace will kick in and I hear it "flaming up" and then the fan goes on.

So basically, I do that before going to sleep and before i leave in the mornings, but the furnace is staying on for less and less time now.

Any advice would be greatly appreciated.


gunit is offline  
 
Reply With Quote
Old 12-29-2008, 12:27 PM  
glennjanie
Senior Member
Join Date: Mar 2006
Posts: 2,990
Liked 4 Times on 4 Posts

Default

Welcome Gunit:
First check the limit switches and relays for proper function. Check the vent flue from the burner to the roof and rid any bird nests or spider colonies.
If the furnace has a board in it, you could check the board for burned spots, chared resistors and transistors.
One member recently went through a long list of troubleshooting and finally discovered the door switch was not engaging properly.
Glenn


glennjanie is offline  
 
Reply With Quote
Old 01-01-2009, 09:36 AM  
d.scott
Junior Member
Join Date: Jan 2009
Posts: 1
Default furnace advice

if this is a gas furnace,which i am assuming,your problem, is in limit switch.when you diconnect power,reset,this resets limit switch.problem could be many things.time to call a tech. d.scott
d.scott is offline  
 
Reply With Quote
Old 01-10-2009, 04:17 PM  
Icehouse
Junior Member
Join Date: Jan 2009
Posts: 10
Default

See below

1. Thermostat calls for heat.

2. Draft inducer motor starts.

3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes.

4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas.
Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem.
The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Icehouse is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Is outside air really needed for a furnace? berricks HVAC 15 06-04-2014 09:01 PM
Gas Furnace Maintenance Icehouse HVAC 4 02-17-2012 01:32 PM
lux air furnace duane HVAC 3 01-04-2010 08:06 PM
Attic Furnace remodel101 HVAC 0 02-08-2007 12:20 AM