Gas furnace igntion problem

House Repair Talk

Help Support House Repair Talk:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

uilleann13

New Member
Joined
Jan 15, 2009
Messages
1
Reaction score
0
I have an intermittent ignition problem with my 8 yr old Nordyne furnace. The ignition sequence proceeds as follows -

The ignitor glows and the flame lights for a few seconds but does not fire the main burners. The sequence repeats up to 4 times and the furnace either fires up or locks out with an ignition failure code. It tries again an hour later or if I notice the problem, powering on and off restarts the sequence and it will usually fire up the second time around.

There are no other error codes on the board so the limit circuit isn't opening and I've replaced the ignitor and flame sensor.

Any ideas. It worked perfectly when an engineer looked at it, but he suggested that the burners may be corroded. Does that make sense and how can I fix it?
 
Welcome Uilleann:
Yes, the burners could stand a little wire brushing and make sure you can see light through hole (shine a light in the end of the burner and look through each hole). It must be an induced draft model and there may be something in the vent pipe. If it can't move enough air through the vent, it will shut down.
Glenn
 

Latest posts

Back
Top