The wiring diagram I am speaking of is the smaller of the two pictures on post #4, using 3 wire between Light fixtures.


Mattr is offline  
 
Reply With Quote
Old 04-09-2014, 09:58 PM  
nealtw
Contractor
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,804
Liked 1399 Times on 1233 Posts
Likes Given: 2408

Default

Take one wire off the switch, do the lights go off? Test the switch, does the switch open?


nealtw is offline  
 
Reply With Quote
Old 04-10-2014, 06:53 AM  
JoeD
Contractor
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 1,096
Liked 138 Times on 112 Posts
Likes Given: 4

Default

Connect the fixture and see what happens. It will either be on or off all the time or work properly. You will not cause and harm.

If you are using a digital meter you could be getting a false reading called phantom voltage.
JoeD is online now  
 
Reply With Quote
Old 04-10-2014, 08:33 AM  
nealtw
Contractor
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,804
Liked 1399 Times on 1233 Posts
Likes Given: 2408

Default

Quote:
Originally Posted by JoeD View Post
Connect the fixture and see what happens. It will either be on or off all the time or work properly. You will not cause and harm.

If you are using a digital meter you could be getting a false reading called phantom voltage.
In post 10 he did that and the lights stayed on.
nealtw is offline  
 
Reply With Quote
Old 04-10-2014, 08:54 AM  
Wuzzat?
Banned
Join Date: Jan 2010
Posts: 2,328
Liked 168 Times on 155 Posts
Likes Given: 94

Default

For one switch controlling two lights the basic circuit is that
the lights are in parallel (assembly 1),
the switch and the power source are in series (assembly 2),
and these two assemblies are in series.

In addition, the lamp socket center contact should be hot (120v above ground) so that the threaded shell which is more accessible to the user is close to ground.

What gets messy is having the additional constraint of having the wire colors correspond to some version of the electrical code so future workers know what you did.
Houses don't seem to come with schematics or wiring diagrams; the wire colors are the diagram.

For further confusion: are outlets in a branch circuit in series or in parallel?
I'd say the hot sides (short slots) are in series and
the neutral sides (long slots) are in series but
each outlet is in parallel with the others.

Last edited by Wuzzat?; 04-10-2014 at 09:36 AM.
Wuzzat? is offline  
 
Reply With Quote
Old 04-10-2014, 11:18 AM  
Mattr
Junior Member
Join Date: Apr 2014
Posts: 4
Default all fixed...

just took off one wire from the switch and i have juice on both sides, so i determined that the switch is bad. Replaced it and we are good. Thanks Nealtw for pointing that out...
Mattr is offline  
 
Reply With Quote
Old 04-10-2014, 11:45 AM  
nealtw
Contractor
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,804
Liked 1399 Times on 1233 Posts
Likes Given: 2408

Default

That is what I was hoping for but I was afraid you had bigger things happening.
nealtw is offline  
 
Reply With Quote
Old 04-10-2014, 11:58 AM  
Wuzzat?
Banned
Join Date: Jan 2010
Posts: 2,328
Liked 168 Times on 155 Posts
Likes Given: 94

Default

Quote:
Originally Posted by nealtw View Post
That is what I was hoping for but I was afraid you had bigger things happening.
And the OP might well have. . . This was lucky.

A wire coming out of a wall could go to hot, neutral, ground, the upstream or downstream side of a switch or a load like a lamp or an appliance or to nothing at all and so you'd get a phantom voltage.
Checking for each can be tedious, especially when your tester gives you false readings.

If I had only one tester it'd be a high wattage 240v bulb or two 120v bulbs in series. A single 120v bulb will do but you run the risk of putting it across 240v. Which reminds me, wear eye protection and if you are really risk-averse, wear face protection.

Last edited by Wuzzat?; 04-10-2014 at 12:02 PM.
Wuzzat? is offline  
 
Reply With Quote
Old 04-10-2014, 12:15 PM  
nealtw
Contractor
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,804
Liked 1399 Times on 1233 Posts
Likes Given: 2408

Default

Quote:
Originally Posted by Wuzzat? View Post
And the OP might well have. . . This was lucky.

A wire coming out of a wall could go to hot, neutral, ground, the upstream or downstream side of a switch or a load like a lamp or an appliance or to nothing at all and so you'd get a phantom voltage.
Checking for each can be tedious, especially when your tester gives you false readings.

If I had only one tester it'd be a high wattage 240v bulb or two 120v bulbs in series. A single 120v bulb will do but you run the risk of putting it across 240v. Which reminds me, wear eye protection and if you are really risk-averse, wear face protection.
Let's not go to panic mode to fast. He said, he understude the diagram and followed correctly, that only left the switch. I would not have suggested hooking up the lights in case he had a 220 situation but more likely a mistake would have been 2 sources from the same breaker.
Sometimes the best answer is nothing better than better questions.
nealtw is offline  
Wuzzat? Likes This 
Reply With Quote
Old 04-10-2014, 01:15 PM  
Wuzzat?
Banned
Join Date: Jan 2010
Posts: 2,328
Liked 168 Times on 155 Posts
Likes Given: 94

Default

Quote:
Originally Posted by nealtw View Post
Let's not go to panic mode to fast. He said, he understude the diagram and followed correctly, that only left the switch. I would not have suggested hooking up the lights in case he had a 220 situation but more likely a mistake would have been 2 sources from the same breaker.
Sometimes the best answer is nothing better than better questions.
One time I figured out how many ways you could hook one, two or three wires to an outlet that has hot, neutral and ground.
Just listing them was exhaustive and amounted to about 30 ways, which means your odds of getting it right by guessing was about 1 in 30.
Of course, DIYers know stuff (some right and some wrong) and so the odds are considerably better but still in favor of Murphy's Law.

IIRC a book on troubleshooting said to take one guess and then get back to basics and follow the tried and true troubleshooting routines, tedious and slow as they may be.
http://www.google.com/search?client=...UTF-8&oe=UTF-8
You trade slowness for certainty.

My guesses, and those of people on forums who fix by replacing parts, are hardly ever right so almost immediately I start checking the basics.
It follows from this that learning the basics will almost always serve you, sooner or later. And knowing these means you hardly ever panic.

A few times I ran into 'impossible' situations, which I soon learned meant that I was assuming something that was not true. Finding that unconscious assumption of mine was real work.



Last edited by Wuzzat?; 04-10-2014 at 01:23 PM.
Wuzzat? is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Shop Lights croast Electrical and Wiring 2 02-20-2008 09:45 PM
No Lights Jed54 Electrical and Wiring 1 02-07-2008 11:06 PM
lights are dimming zoglchaim Electrical and Wiring 3 10-24-2007 06:44 PM
how many lights on a single light switch? Philphine Electrical and Wiring 8 04-17-2007 10:54 AM
patio lights jdc50 Electrical and Wiring 1 03-08-2006 06:23 PM

Newest Threads

LATEST SPONSOR DEALS