Default 1890 house wiring issues. Help!

So I've been doing a renovation on an 1890 house for the past several years, but I haven't done anything to the electrical in the house for at least the last year.

The problem is that suddenly, last weekend, the breaker for the circuit that powers all the lights on the first floor started tripping. Nothing was done to provoke this reaction (no new wiring/extra appliances added to the circuit/etc.). I called an electrician and he used an ammeter to determine that the circuit was pulling 60 amps for the short time that it would stay on.

Oh, and I should mention that it wasn't tripping immediately. It would go on and produce an audible humming inside the breaker panel and then trip after 5 to 10 seconds.

The electrician was unable to remedy the problem, but he was able to isolate the offending leg of the circuit by disconnecting it at a junction just inside the house from the breaker panel. So I have a few lights on the first floor, but the majority of the lights are still not operational.

So basically the mystery is: sudden onset of breaker tripping, circuit pulling 60 amps for no known reason, circuit seems to need to "charge up" to the point of tripping the breaker (ruling out a direct short somewhere in the line).

I am at a loss on this one and apparently so was the electrician I called. I have accepted that I may need to pigtail off of other circuits in the rooms with the non-working lights, but I thought I would take a stab and see if anyone here has encountered a similar problem.

Please help if you can.

Thanks.



__________________
thewhistler is offline  
 
Reply With Quote Quick reply to this message
Old 11-02-2009, 08:40 PM  
Roger I.
Junior Member
 
Join Date: Nov 2009
Posts: 3
Default

I had something similar several years ago. It ended up being a shorted wire in a ceiling fan that finally shorted out over a period of years from the vibration.

Other than that all you can do is at the pigtails. divide and conquer sorta like using a roadmap..

I hope this helps.



__________________
Roger I. is offline  
 
Reply With Quote Quick reply to this message
Old 11-03-2009, 06:07 AM  
inspectorD
Housebroken
HRT_MODERATOR.png
 
inspectorD's Avatar
 
Join Date: Dec 2005
Location: Litchfield, CT
Posts: 4,091
Liked 125 Times on 105 Posts
Likes Given: 318

Default well

It could be as simple as varmints. Mice like to peel back the coverings of older wire, easy to peel and makes for a warm nest. Then the little buggers go and make contact with the wire and become very grounded.
Find them all the time. Try to isolate the wire with the issue and start your rewiring sooner than later.
These are the cause some house fires.

__________________

Just My
Made in the

inspectorD is offline  
 
Reply With Quote Quick reply to this message
Old 11-03-2009, 07:31 AM  
travelover
Senior Member
 
Join Date: Aug 2007
Posts: 693
Liked 2 Times on 2 Posts

Default

I agree, if you have the old knob and tube or even the cloth covered wire you have an unstable situation. Best to take care of that so that you have peace of mind.

__________________
travelover is offline  
 
Reply With Quote Quick reply to this message
Old 11-03-2009, 07:02 PM  
rdmayers
Junior Member
 
Join Date: Oct 2009
Posts: 12
Default

Do you Know exactly what is on the circuit, and how far did the electrician trace it before he gave up. It sound like you have circuit breaker so some of the electrical has already been ungraded. Are you dealing with knob and tube or romex. if it is romex does it include a ground wire. Have you tried a ohm meter to trace the circuit. it sound like you have a circuit that is either going to ground or from hot to nuteral. Are you dealing with a grounded circuit. Is this circuit just lighting or are there outlets on the circuit as well. If there is outlets on the circuit the problem may be with something you have plugged into the circuit.

__________________
rdmayers is offline  
 
Reply With Quote Quick reply to this message
Old 12-20-2009, 12:06 AM  
lou19604
Junior Member
 
Join Date: Dec 2009
Posts: 12
Default

GHOST???

A) BAD BREAker

B) A SMALL PART OF THE WIRE HAS BECOME COOKED THE REASON IT SEEMS TO "CHARGE UP THEN POP" IS ALONG THAT WIRE SOMETHING HAS COME IN CONTACT WITH THE COPER (DURING REMODLING ITS NOT UNCOMMON TO STRAFE A WIRE USUALY BY A NAIL) AND HAVE THIS PROBLEM CHECK THE PREVIOS DAYS WORK AND SEE IF YOU COUL OF DONE THAT



__________________
lou19604 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
House purchasing issues-Bank going bankrupt CityLimit General Home Improvement Discussion 6 06-17-2009 12:25 PM
1890 house with problematic kitchen - suggestions? cojo General Home Improvement Discussion 2 12-24-2008 03:02 PM
Cost of wiring a house for TV / Net cheesefood Electrical and Wiring 4 11-10-2008 10:47 AM
House to Barn wiring job wtdboss01 Electrical and Wiring 5 04-19-2008 03:09 PM
Aluminum wiring throughout the house ITParalegal Electrical and Wiring 5 06-04-2007 01:02 PM

Newest Threads

LATEST SPONSOR DEALS