Old 12-29-2009, 08:52 PM  
am3rican
Junior Member
 
Join Date: Dec 2009
Posts: 1
Default Roof / Attic Mold

We purchased a house this April in Pennsylvania. We hired a reputable inspection firm to do the inspection. We purchased the house, mainly because it needed relatively little work. In fact, the inspector mentioned the roof was relatively new and was, by his estimate, less than 5 years old. However, several weeks ago we noticed water stains and water dripping from our master bathroom. The roofer we hired to fix the leak cut out 2 5x5 sections of the roof. It was discovered that the plywood under the shingles were covered in mold. Furthermore, he mentioned that while the shingles were new, the plywood was warped, discolored, and cracked namely because poor ventilation had caused the plywood to warp and crack from heat.

I have never sued anyone but feel the inspection company should have discovered that the plywood under the shingles was visibly warped, cracked, discolored, and festered with mold. The inspector did climb into the attic, but only enough to poke is head up there. I also have a sneaking suspicion the seller of the house failed to disclose this because there's obvious evidence in the master bathroom, where it has been leaking, that the ceiling had been patched in several place. At this point, the roofer is quoting me $9000 to replace the plywood and shingles. Do I have any legal recourse? What should I, as the homeowner, do in order to prevent the mold from spreading?

I have a ridge vent running the length of the roof. 2 foot soffits on either side of the house and a gable vent. I can't see how ventilation is a problem but according to the roofer it is.



__________________
am3rican is offline  
 
Reply With Quote Quick reply to this message
Old 12-30-2009, 01:55 PM  
PostSidingLLC
Junior Member
 
PostSidingLLC's Avatar
 
Join Date: Dec 2009
Posts: 6
Send a message via Skype™ to PostSidingLLC
Default Attic ventilation

Quote:
Originally Posted by am3rican View Post
We purchased a house this April in Pennsylvania. We hired a reputable inspection firm to do the inspection. We purchased the house, mainly because it needed relatively little work. In fact, the inspector mentioned the roof was relatively new and was, by his estimate, less than 5 years old. However, several weeks ago we noticed water stains and water dripping from our master bathroom. The roofer we hired to fix the leak cut out 2 5x5 sections of the roof. It was discovered that the plywood under the shingles were covered in mold. Furthermore, he mentioned that while the shingles were new, the plywood was warped, discolored, and cracked namely because poor ventilation had caused the plywood to warp and crack from heat.

I have never sued anyone but feel the inspection company should have discovered that the plywood under the shingles was visibly warped, cracked, discolored, and festered with mold. The inspector did climb into the attic, but only enough to poke is head up there. I also have a sneaking suspicion the seller of the house failed to disclose this because there's obvious evidence in the master bathroom, where it has been leaking, that the ceiling had been patched in several place. At this point, the roofer is quoting me $9000 to replace the plywood and shingles. Do I have any legal recourse? What should I, as the homeowner, do in order to prevent the mold from spreading?

I have a ridge vent running the length of the roof. 2 foot soffits on either side of the house and a gable vent. I can't see how ventilation is a problem but according to the roofer it is.
Even though you have ridge vents, make sure that your 2' soffit overhangs have a ventilation slot cut continuously from end to end (or spaced vents), and that ceiling insulation installed in the joists is not blocking airflow into the roof rafter bays. This provides an air "intake" to the attic and the "exhaust" is through the ridge vent. Ridge vents only work to their full design when they have an intake at the bottom edge of the roof slope.

Most home inspectors usually have so many disclaimers in their reports that any "recourse" is nil. When buying any existing home I always recommend that the roof and the attic be inspected by a professional roofer. Most home inspectors are notoriously weak in their knowledge in this area, and just give it a "quick look".
Ron


__________________
PostSidingLLC is offline  
 
Reply With Quote Quick reply to this message
Old 01-02-2010, 06:46 AM  
stevensonjames88
Junior Member
 
Join Date: Dec 2009
Posts: 14
Default

The best thing would be have a good ventilation in that area. Although it would a bit easy to take out the mold, the problem would be how to totally eradicate them since they would grow again with the presence of moisture.

__________________

[url=http://www.getmoldremovaltips.com][b]Mold Removal Tips[/b][/url]

stevensonjames88 is offline  
 
Reply With Quote Quick reply to this message
Old 01-02-2010, 09:35 PM  
GBR
Senior Member
 
Join Date: Mar 2009
Posts: 343
Liked 21 Times on 20 Posts
Likes Given: 9

Default

As mentioned, you need a balanced ventilation system.
1. figure your square footage and divide by either 1/100, best; 1/150, minimum per code, or 1/300 (with a vapor barrier in attic facing heat). Air Vent: Continuous Soffit Vents Specifications
2. Compare vent styles to brand name for math figures; ridge vent-NFVA sq.in.per foot, soffit vent types and NFVA per each unit or footage. http://www.fureyco.com/content/image...ng_The_Air.pdf
3. The gable vent is short-circuiting the ridge vent causing the soffit vents harm: Audel Complete Building Construction - Google Books
4. The soffit vents (intake) should be close to 9 sq.in. per ft. x each house side = 18, which should equal the sq.in. of ridge vents (exhaust). The gable vent should be plugged. I presume the mold was below or close to the gable vent (same end of house)? Do the math and reply back on how much you have.... Check for this: BlockTheHeat.com -Attic Ventilation Problems The best way is from the attic looking for clear soffit vents, one in each bay between rafters. No insulation interfering with air path to ridge, hopefully baffles installed and blocking against wind-washing the insulation over the outside walls. Pictures would be nice from inside attic area.

Be safe, Gary

__________________
GBR is offline  
 
Reply With Quote Quick reply to this message
Old 01-03-2010, 09:16 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,229
Liked 116 Times on 101 Posts
Likes Given: 65

Default

Make sure that your bathroom exhaust fans exhaust through the roof and not to the soffit. The moist air can be sucked back in through the soffit and cause mold.
As far as recourse, the home inspector might have an E&O clause (errors and omissions).
You have to be able to prove that the seller had knowledge of this condition but, failed to disclose. This is very difficult to prove. Your best bet is if you purchased or were provided a home warranty but, this may also not be covered.



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Shoudl the attic roof be insulated? Todd-Beaulieu Roofing and Siding 7 09-08-2009 02:05 PM
Need help with leak and mold through patio roof madmaxmedia Roofing and Siding 8 03-21-2009 07:22 PM
How to attach roof over deck to house roof. Fran Introductions 4 12-16-2007 08:09 PM
Adding Attic/Roof Ventilation? 1parkpointer Roofing and Siding 4 12-07-2007 01:08 PM
Hello, Looking for suggestion, possible roof leak, mold etc R1000 Roofing and Siding 9 09-25-2007 11:52 PM

Newest Threads

LATEST SPONSOR DEALS