Default Carrier furnace fan won't switch on

I have a 10 year old Carrier furnace. When in heat/ac mode the fan will work, but it won't run continuously in "on" mode. When the heat/ac is "off", and the fan is "on", it won't work at all. It used to work continuously when in "on" mode. The blower motor was replaced a few months ago and the problems started then. The LED light is not showing any problems. Is there a quick fix?



__________________
Augment is offline  
 
Reply With Quote Quick reply to this message
Old 04-07-2010, 02:19 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,213
Liked 115 Times on 100 Posts
Likes Given: 65

Default

Check to see if the green wire or wire from the G terminal on the thermostat is hooked up and likewise at the thermostat terminal connections inside the furnace.



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 04-07-2010, 03:09 PM  
Augment
Junior Member
 
Join Date: Apr 2010
Posts: 22
Default

yes, the green wire is hooked up on the thermostat and the furnace.

__________________
Augment is offline  
 
Reply With Quote Quick reply to this message
Old 04-07-2010, 03:45 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,213
Liked 115 Times on 100 Posts
Likes Given: 65

Default

What happens when you jumper 24V from the red wired to the green wire?
If you remove the furnace panel door, make sure the safety switch doesn't cut power to the unit while testing.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 04-07-2010, 03:51 PM  
Augment
Junior Member
 
Join Date: Apr 2010
Posts: 22
Default

I wouldn't know how to do that - please explain!

__________________
Augment is offline  
 
Reply With Quote Quick reply to this message
Old 04-07-2010, 04:24 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,213
Liked 115 Times on 100 Posts
Likes Given: 65

Default

Oh sorry, sometimes I assume too much.
Take a piece of wire and strip the two ends.
Touch one end to the "R" terminal and the other end to the "G" terminal on the thermostat terminal strip inside the furnace.
As I mentioned, there may be a safety switch that will kill power to the unit when the access panel is removed. For the most part, you can just hold this in to restore power while testing.
Jumpering the R&G should run the blower motor.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 04-07-2010, 08:26 PM  
Augment
Junior Member
 
Join Date: Apr 2010
Posts: 22
Default

What would I be achieving by doing this? I'm reluctant to try anything without knowing why I'm doing it. The blower motor does work if it's in heat mode, just doesn't stay on continously even tho the fan setting on the thermostat is set to "on".

__________________
Augment is offline  
 
Reply With Quote Quick reply to this message
Old 04-07-2010, 09:43 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,213
Liked 115 Times on 100 Posts
Likes Given: 65

Default

I'm trying to guide you in troubleshooting the circuitry of the unit. This will basically tell us if the T-stat is bad or if there are other issues preventing the fan from working in the "On" setting. It's only 24VAC so no safety issues to be concerned about. If you prefer an alternate technique, you'll need a voltmeter. Turn your tstat to fan "On" and check for 24VAC from ground to "G" (green). This will tell me if the tstat is energizing the fan circuit or we can just energize it and see if the fan comes on which is what I was attempting in my prior post.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 04-07-2010, 09:58 PM  
Augment
Junior Member
 
Join Date: Apr 2010
Posts: 22
Default

I don't have a voltmeter, but will attempt the test tomorrow. If the fan is energized this way, does it mean the tstat is bad?

__________________
Augment is offline  
 
Reply With Quote Quick reply to this message
Old 04-08-2010, 06:43 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,213
Liked 115 Times on 100 Posts
Likes Given: 65

Default

If the fan turns on as a result of the test, it will either be a bad Tstat or the wiring from the Tstat to the furnace.
If you'd like, you can jumper the R & G terminals on the back of the Tstat and this will verify the wiring and result in determining a bad Tstat.



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Carrier Model # FB4ANF048 djones4506 HVAC 4 02-09-2010 08:07 PM
Carrier Thermostat viletha HVAC 5 02-07-2010 09:57 PM
Pilot burner replacement - Carrier 58GS150-CB furnace danielr HVAC 0 09-16-2009 10:39 PM
Carrier Thermidistat sailpe HVAC 1 08-17-2009 09:26 AM
Carrier gas furnace blows cold air tepolt HVAC 5 03-26-2008 04:25 PM

Newest Threads

LATEST SPONSOR DEALS