Default Inaccessible AC Drain line

Howdy, all.

I've got a clog in my AC drain line, but the trouble that I'm having is that the drain line empties in an inaccessible location. It drops down through the wall and is connected via PVC pipe to the drain line of a bathroom sink.

I'm a bit reluctant to try to use a shop-vac to pull out the clog through the T in the drain-line, but is this my only other option?

I can send some pictures if those would aid in the description. Let me know, thanks!



__________________
brimhack is offline  
 
Reply With Quote Quick reply to this message
Old 07-07-2010, 06:56 AM  
CraigFL
Senior Member
 
Join Date: Mar 2006
Posts: 409
Default

I blow mine out with pressure from my air compressor every so often. I keep the pressure below 40psi when I do it...



__________________
CraigFL is offline  
 
Reply With Quote Quick reply to this message
Old 07-07-2010, 09:06 AM  
brimhack
Junior Member
 
Join Date: Jul 2010
Posts: 4
Default

I tried doing that through the access "T" in the drain line, but rather than loosening the clog, it just blew air straight back into the condensate pan.

Although I suppose I could cut a section of the drain line after the "T", blow the air in there and then put the whole thing back together.

__________________
brimhack is offline  
 
Reply With Quote Quick reply to this message
Old 07-07-2010, 10:09 AM  
CraigFL
Senior Member
 
Join Date: Mar 2006
Posts: 409
Default

You need to seal the tee off so it only blows through the drain line. I have a short piece of auto heater hose that's just the right size to jam into the ID of the drain pipe. You then need a seal so that you just don't blow air down the hose but have it sealed off so you actually pressurize the line to force the clog out.

__________________
CraigFL is offline  
 
Reply With Quote Quick reply to this message
Old 07-07-2010, 12:08 PM  
brimhack
Junior Member
 
Join Date: Jul 2010
Posts: 4
Default

I tried to a diagram of what my setup looks like...



The problem I have, even when I have a strong seal around the compressed air hose, is that there's no chance for the drain line to get pressurized: it just blows out the end that drips into the condensate pan. And I just now realized that the same problem would apply with a shop-vac.

Unfortunately, there's no access to either end of the drain pipe. The insides of the AC unit are sealed so I can't access the section that ends at the condensate pan, and the other end drains into the bathroom sink drain line.

__________________
brimhack is offline  
 
Reply With Quote Quick reply to this message
Old 07-07-2010, 04:23 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,214
Liked 115 Times on 100 Posts
Likes Given: 65

Default

Have you tried a plumbing snake or an electrial fish tape?

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 07-07-2010, 09:38 PM  
oldognewtrick
Moderator
HRT_MODERATOR.png
 
oldognewtrick's Avatar
 
Join Date: Jul 2009
Location: Nashville, TN
Posts: 5,685
Liked 494 Times on 411 Posts
Likes Given: 150

Default

Armchair quarterback, oldog/newtrick thinks KOK has the right idea, or cut the pipe after the tee and put some pressure there.

Unfournately I understand your diagram.... oh so well...sigh...

__________________
oldognewtrick is offline  
 
Reply With Quote Quick reply to this message
Old 07-14-2010, 11:00 AM  
brimhack
Junior Member
 
Join Date: Jul 2010
Posts: 4
Default

The snake seems to have done the trick, knock on wood! Thanks for the help, fellas!

__________________
brimhack is offline  
 
Reply With Quote Quick reply to this message
Old 07-14-2010, 02:54 PM  
inspectorD
Housebroken
HRT_MODERATOR.png
 
inspectorD's Avatar
 
Join Date: Dec 2005
Location: Litchfield, CT
Posts: 4,093
Liked 125 Times on 105 Posts
Likes Given: 319

Default what?

Quote:
Originally Posted by oldog/newtrick View Post
.Unfortunatly I understand your diagram.... oh so well...sigh...
You mean the part about the clog and the commpressed air?? Does that upset your wife too?

Glad you found the fish...and cleaned your pipe.
__________________

Just My
Made in the

inspectorD is offline  
 
Reply With Quote Quick reply to this message
Old 07-14-2010, 04:22 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,214
Liked 115 Times on 100 Posts
Likes Given: 65

Default

Job well done!



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Underground downspout drain line edlank General Home Improvement Discussion 3 04-07-2009 05:25 PM
Drain line thermal expansion ticking edlank Plumbing Forum 2 03-26-2009 07:18 AM
Freezing drain line johnnyboi1016 Plumbing Forum 8 09-20-2007 08:48 AM
gas line shovelshort Plumbing Forum 6 03-13-2007 04:27 PM
Sewer drain line question Texasguy Plumbing Forum 6 07-03-2006 04:43 PM

Newest Threads

LATEST SPONSOR DEALS