I've been working on adding a sub panel to my shop. I have a two pole 100amp sub panel. I'm looking for someone to explain a bit of how load is distributed in the sub panel the two poles.
I know that for 100 amps i need at least #3 awg THHN copper to handle the load but my question is about how that load is distributed. If i have a two pole 100amp breaker in the main panel feeding my two pole 100amp sub panel isn't the potential amp load distributed evenly between the poles? If i'm drawing 30 amps on a two pole breaker in the sub-panel is that 30 amps of draw being evenly distributed into two 15amp loads on each pole?
I'm already going to run 3awg copper for both hots and the neutral but i want to understand the theory behind how this works. Anyone who feels like putting on their professor hat would be greatly appreciated.
I know that for 100 amps i need at least #3 awg THHN copper to handle the load but my question is about how that load is distributed. If i have a two pole 100amp breaker in the main panel feeding my two pole 100amp sub panel isn't the potential amp load distributed evenly between the poles? If i'm drawing 30 amps on a two pole breaker in the sub-panel is that 30 amps of draw being evenly distributed into two 15amp loads on each pole?
I'm already going to run 3awg copper for both hots and the neutral but i want to understand the theory behind how this works. Anyone who feels like putting on their professor hat would be greatly appreciated.