120 v outlets at 108 static

Discussion in 'Electrical and Wiring' started by stlsig, May 30, 2010.

  1. May 30, 2010 #1

    stlsig

    stlsig

    stlsig

    New Member

    Joined:
    May 30, 2010
    Messages:
    2
    Likes Received:
    0
    Today my AC stopped working correctly. The compressor was working, but the fans, while clearly getting electricity, wouldn't kick on. My HVAC man (who has serviced these units for 30 years) tested the electric coming into the fans. This is a 120 v circuit and with the fans off it was drawing about 108 v and then once we kicked the fans on, it dropped to 105 v. Thus there wasn't enough electric to get the fans on.

    FYI - After the fact, The HVAC man took one fan home to test it, it worked fine.

    We then tested all the other outlets in the house and sure enough, they are all drawing the same voltage. We also tested the convenience outlet at the main panel, same results.

    Does anyone have an idea what is causing this? We cant get the AC operational until this is fixed and I'm concerned that it might be a much lager issue than just one circuit.

    Thanks,
     
  2. May 30, 2010 #2

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    If your at all comfortable working with electricity; remove the cover panel from you load center and check voltage from leg1 to ground, leg1 to neutral, leg2 to ground, leg2 to neutral and leg1 to leg2 (for 240V).
    If these check out to be 120V then you have a problem with your load center and need to check for loose connections and/or call an electrician.
    If they check out to be 108V then you have a problem with your service and need to call your local utility provider.
     
  3. May 30, 2010 #3

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    Yeah, it's a high resistance upstream of your AC, possibly caused by a loose connection.

    Being careful of arc-flash, and using a 20A, 240v load like a wall oven or an elec. dryer, measure the 240v at the panel.
    When you switch off the wall oven the voltage should go up no more than ~0.4vac. You'll need a DVM to measure a change this small.
    You're looking for the change in voltage. It may be somewhat larger than 0.4vac, depending on how far away you are from the pole transformer.
     
    Last edited: May 30, 2010
  4. May 31, 2010 #4

    stlsig

    stlsig

    stlsig

    New Member

    Joined:
    May 30, 2010
    Messages:
    2
    Likes Received:
    0
    I have an electrician coming tomorrow to check everything out. I appreciate all of your knowledge.
     
  5. May 31, 2010 #5

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,528
    Likes Received:
    273
    Call the POCO. It is likely it is their problem. Did the HVAC tech measure the 240 volts? I bet it was low as well.
     