    Hi:

    Porter-Cable CPLMC7580V2C 7.5 HP 80 gallon industrial 2 stage compressor.

    Specs:
    Voltage/Hertz/Phase: 240/60/1
    Horse Power: 11.00 peak, 7.5 run
    30 Amps @ 240 Volts.

    Instructions say "minimum branch circuit requirement" : 30 amp.

    I'm leaning towrads using a 40 amp breaker, 8-2 wire w/ground.
    Does this seem right? I'm concerned if I used a 30 amp breaker
    with 10-2 wire it might trip the breaker when it kicks in.
    It's only about 35 to 40 feet away from the electric panel.

    Now also thinking about this idea: wire it up with a 50A breaker and 6AWG wire and NEMA 6-50 recepticle and put a NEMA 6-50 plug on the compressor. That way I can also use the recepticle for a Lincoln 220 welder
    that has a NEMA 6-50 Plug requiring 50 Amp circuit and a Lincoln 180C welder that came with a NEMA 6-50 Plug requiring a 40 AMP circuit.
    This would save me from running a line for the welders. I would never
    use the compressor or any of the welders at the same time.
    Just wondering if using a 50 AMP breaker is too much for the compressor
    by not providing enough safety by not being able to trip if or when needed.

    Thanks !
     
  2. Jan 16, 2008 #2

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    All the industrial compressor I've worked with are 3 phase not single. They are also setup to run constantly with load and unload pressure points that keep a steady supply of air in the tank. Your unit should state the FLA and that will determine the amperage required.
     
  3. Jan 17, 2008 #3

    guyod

    guyod

    guyod

    Senior Member

    Joined:
    Jan 12, 2008
    Messages:
    423
    Likes Received:
    21
    Installing a sub panel might be a little more work but would allow you to use both plus what ever toys your get in the future.
     
  4. Jan 17, 2008 #4

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    This is NOT an "industrial" compressor. It is a P-C compressor with the word "Industrial" on it. There IS a difference.

    Also, the ones you are referring to a pretty rare, at least around here. In fact I have never even seen one that runs constantly. Pretty wasteful IMO, I don't care how mush it is used.

    First off, this is NOT a true 7.5hp motor if it is only a 30A draw. A "real" 7.5hp motor @ 240v single phase should be around a 38-40A draw.
    This is probably one of those "developed HP" ratings, like Craftsman shop vacs have. We ALL know, there is no such thing as a 6hp shop vac with a standard 15A plug on it. :p


    Scot,
    If the actual draw is 30 amps then DO use #8 wire and a 40 amp breaker.

    There are MANY odd and special codes regarding motors. Read NEC Art. 430. Your head will spin.
     
  5. Jan 17, 2008 #5

    guyod

    guyod

    guyod

    Senior Member

    Joined:
    Jan 12, 2008
    Messages:
    423
    Likes Received:
    21
    I fell for the developed hp rating on the shop vacss . i cant believe i every fell for that. I remeber thinking " i dont think 3hp is strong enough for what i need better go for the 6hp " lol
     
  6. Jan 17, 2008 #6

    Scot Clark

    Scot Clark

    Scot Clark

    Member

    Joined:
    Aug 29, 2006
    Messages:
    17
    Likes Received:
    0
    Hi Folks: Thanks again for the advise.
     
  7. Jan 30, 2008 #7

    triple D

    triple D

    triple D

    Well-Known Member

    Joined:
    Jan 30, 2008
    Messages:
    296
    Likes Received:
    1
    If you have a name plate rating on a lift or a compressor or a shop vac. or any g.darn thing wire for the name plate rating. 30 amps is 10 ga. wire.... if it says 30 amp min circ size, this doesnt mean you will catch on fire, or that the breaker will need frequent resetting!!!!! Have you seen the price of wire lately fellas??? If a name plate rating is above a division of 10 (examp. 33 amps) round up to next breaker as 30 wont work If plate says max. rating you may need fuseable disconnect to hit something like 35 amp or 45 amp. And hel& no dont run it on 40 or 50 amp this is over fed and unsafe!!!! Put plug for welder closer to panel, it will be cheaper. compressor needs 30 amp 240volt breaker and 10ga wire copper.
     