AC system not working...

Discussion in 'HVAC' started by beachguy005, Aug 3, 2013.

  1. Aug 3, 2013 #1

    beachguy005

    beachguy005

    beachguy005

    Well-Known Member

    Joined:
    Sep 25, 2012
    Messages:
    844
    Likes Received:
    310
    Hi folks, I have a 12 year old Ruud system that started blowing warm air. Checking outside on the unit and the fan motor had stopped turning, though it's not seized. Compressor seemed to be working. Contactor was chattering as it has been. I'm going to check the capacitor when I get my bud's meter. I'm trying to figure the correct methodology if the cap is good, test the motor? Anything else I should be looking at? I'm in S Florida, if it matters. Thanks,
     
  2. Aug 3, 2013 #2

    CallMeVilla

    CallMeVilla

    CallMeVilla

    Well-Known Member

    Joined:
    Feb 9, 2010
    Messages:
    1,651
    Likes Received:
    594
    Most common problem is blown capacitor. Remember to discharge it before touching it. Use a pair of pliers or a screw driver to ground both the Herme and the Fan poles to the Common. It is good practice to replace the capacitor if there is a AC problmem. They are cheap and easy to repair.

    Next step will be checking the motor. You might find this to be more info than you want ... but you will learn a lot! [ame]http://www.youtube.com/watch?v=yqiHh_Rufi0[/ame]

    Good luck! Stay cool!
     
  3. Aug 6, 2013 #3

    beachguy005

    beachguy005

    beachguy005

    Well-Known Member

    Joined:
    Sep 25, 2012
    Messages:
    844
    Likes Received:
    310
    Got it fixed. Had a couple of hot days waiting for the replacement capacitor but that's all it was. Chillin now.... Thanks,
     
  4. Aug 9, 2013 #4

    CallMeVilla

    CallMeVilla

    CallMeVilla

    Well-Known Member

    Joined:
    Feb 9, 2010
    Messages:
    1,651
    Likes Received:
    594
    You are welcome ....
     