    Hi,

    I have an older house built 1938 which has mostly 2-wire BX wiring throughout.

    I plan on replacing a few polarized 2-prong outlets to 3-prong... and was considering an AFCI receptacle for added safety. I read that some new construction requires this and also because my daughter uses her hair dryer and curling irons in her room I feel that I'd like the extra protection from circuit overloading / fire... with the older house wiring. The outlets I would be replacing with an AFCI are all BX wire with metal boxes.

    My thinking is to us an AFCI receptacle for added safety but then I was reading information that seemed to suggest there were other considerations with how the house was wired from a branch, etc.

    QUESTION: is it appropriate to use a AFCI in a bedroom for this purpose?
    QUESTION: Should I use an AFCI over a GFCI? Think I saw on this old house once where they used a GFI in a bedroom.

    Thanks!
     
    Last edited: Feb 9, 2014
  2. Feb 9, 2014 #2

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    Neither AFCI nor GFCI will protect from overload or short circuit. This is the job of the breaker.

    Now...GFI on ungrounded circuits DOES provide an added level of safety, AND on the LOAD side of a GFI breaker or receptacle you can install 3-prong receptacles. This is a code complaint alternative to re-wiring.
    That said, AFCI will provide an even additional level of safety, but with such older wiring you may get more than normal nuisance tripping.
    If you want it all, you can use an AFCI breaker, and a GFI receptacle at the first receptacle in the circuit. One major problem I find in this scenario is that many older homes like yours are wired in such a way that there is a junction box, typically in a basement light or box in the attic, and the rest of the circuit continues from there with several legs. Similar to a wagon wheel hub and spokes. With this wiring setup you CANNOT use the LINE and LOAD function of a GFI receptacle. You'd need a GFI at nearly every spot.
    Using a GFI breaker, and NOT an AFCI at all would solve this problem and still add a decent level of safety over what you have now..
     
    CallMeVilla, inspectorD and nealtw like this.
  3. Feb 10, 2014 #3

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    My wife has a hair dryer with a GFCI built into the plug and the wall outlet is also a GFCI. So, with these two GFCIs cascaded we get nuisance tripping - but - always with the wall outlet and never with the dryer plug.

    I guess the dryer plug is less sensitive or maybe it doesn't work at all.
    Testing the plug GFCI would require me to run a 16 kilo-ohm resistor from the dryer insides to a ground. Since we already have a GFCI in the wall this is a pretty low priority job for me.

    Anyway, since organizations are somewhat less likely to BS the Patent Office than the general public
    I'd do an online search for patents for GFCI designs that specifically address this tripping problem and
    hopefully you can find a GFCI in a store nearby that incorporates the improved design.
    But, everybody wants to use up old stock first.
     
  4. Feb 10, 2014 #4

    curtish

    curtish

    curtish

    New Member

    Joined:
    Feb 9, 2014
    Messages:
    3
    Likes Received:
    0
    Thanks guys,

    I hear what you are saying but I don't fully understand why an AFCI Receptacle is of no value over a GFI in this situation... (by the way, the curling iron does not have a GFI oddly enough)

    I get that the AFCI can't prevent a circuit overload and that would be the function of the circuit breaker.

    EDIT: It occurred to me that I may be confusing two different kinds of AFCIs. As you know, there are Outlet AFCI Receptacles and AFCI Breakers. I was considering a Outlet AFCI Receptacle...

    QUESTION: What is the proper use of an AFCI receptacle? Should I just be replacing my breaker with a AFCI breaker instead?

    If I can get a AFCI Breaker to replace my SQUARE D breaker, should I assume that would protect the entire circuit? that would be preferred since the same circuit feeds 3 bedrooms.

    From my reading over at Leviton, it would seemed that AFCI Receptacle have circuitry specifically designed to reduce the chance of shorts... whereas a GFI is used to reduce shocks from a poor ground or near water surfaces...

    I'm not worried so much about shocks... I'm thinking more about shorts and a possible poor ground that wouldn't trip the breaker

    Thanks, I think I know my answer just trying to be clear.
     
    Last edited: Feb 10, 2014
  5. Feb 11, 2014 #5

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    If you can get such a thing I'd prefer that over a breaker because it will be much easier to troubleshoot.

    An arc is supposed to be a fourth state of matter: plasma, as distinguished from solid, liquid or gas.
    These gadgets are supposed to distinguish between "good" arcs and "bad" arcs. Practically what this means is that this device will be telling you when to replace your arc-producing appliances and fixtures: motors with brushes and commutators, and switches.
    I'd prefer to make my own judgements of when things are worn out.

    The accuracy of measuring or testing instruments is supposed to be traceable to the NIST, so I asked them if they have "a standard arc", something to compare to.
    They did not reply, probably because it would be bad for business to have official opinions made public about good or bad arcs, false positives/negatives and all kinds of other worms that would climb out of this can.

    I doubt that you will find the truth about how reliable these things are and if they significantly improve fire safety over the base rate of fire danger here in the U.S..
    If I were close to a Tech Library I'd look in the IEEE Transactions on Power or whatever journal is likely to post a study on this.
    Online patent texts may also talk about the shortcomings of earlier AFCI designs.
     
  6. Feb 11, 2014 #6

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,892
    Likes Received:
    3,117
    If you were going to protect the wiring with AFCI you would want to change the breakers to include all the wires not just the outlet. With and older house that is likely going to include a new breaker box.
     
    KULTULZ likes this.
  7. Feb 11, 2014 #7

    curtish

    curtish

    curtish

    New Member

    Joined:
    Feb 9, 2014
    Messages:
    3
    Likes Received:
    0
    Sounds like there are no solid believers in AFCI receptacles for older homes... as it would only protect a device plugged into the AFCI outlet and any extension cords for shorts.

    Although I'm wanting to shore up my older wiring without rewiring the house, seems like a waste of money unless I can determine where the first outlet of a supply branch is and whether there was "wagon wheel hub" extensions in the house.

    I have already run new dedicated 20 amp circuits to bedroom A/Cs and bathrooms. Perhaps I shouldn't worry too much about the other older wiring in the walls.

    I think that's correct anyway, perhaps I will just install a GFI as Speedy Petey recommends.

    Thanks for the advice.
     
  8. Feb 11, 2014 #8

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,892
    Likes Received:
    3,117
    You might spend some time and check the condition of the wires in boxes and map the system then you could intall welll placed gfis.
    In an older house you likely have places that you may be concerned about, extention cords and the like then maybe an afci outlet would not be a bad idea.
    The other thing to watch for in old house. If you had a short from a wire to cast iron or copper or steel pipe it would be grounded and blow the fuse or breaker, but as time goes by and people change parts of the plumbing to plastic and ground is lost. A pipe could be live for years waiting to kill someone.
     
  9. Feb 19, 2014 #9

    gottodo1

    gottodo1

    gottodo1

    Well-Known Member

    Joined:
    Apr 15, 2013
    Messages:
    171
    Likes Received:
    29
    Wuzzat, I'm sure there's information about an Arc. Do you know what AFCI's are certified against, is it an ANSI, ISO etc etc standard? I can find out what the criteria are or at least how they test it if they don't have design criteria.
     
  10. Feb 19, 2014 #10

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    I was unable to find it.
    And as I recall, even the online patents that I searched did not shed much light on exactly how their "signature analysis" is supposed to work. The maker can always claim a Proprietary Method.

    Surely at the end of the assembly line these devices are tested, go/no-go, before sold. I'd hope they are tested against bad arcs and good arcs, but I'd like to see that test setup. And how closely do the test arcs match the real world?

    And it's not just bad arcs. If you know some programming languages, apparently AFCIs work according to
    IF (more than 5A flowing AND bad arc) THEN trip ELSE (don't bother the home owner).
    The current flow is another variable in this arc detection strategy.

    More generally, and knowing about this
    http://en.wikipedia.org/wiki/Sensitivity_and_specificity
    as a limit on how well these things can possibly work, I'd like to see the numbers for AFCIs. Numbers are harder to spin.

    Let's say you have a genuine bad arc inside a lamp switch.
    Well, the switch is housed in a fire resistant shell and a bad switch will make itself known with how the bulb behaves.
    So how many house fires did we have before these things and how many do we have now?

    With GFCIs there is probably a bias in favor of tripping if the thing is in doubt. I've never heard complaints about a GFCI not tripping and the person continuing to get a shock.
     
    Last edited: Feb 19, 2014
  11. Feb 19, 2014 #11

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,892
    Likes Received:
    3,117
  12. Feb 20, 2014 #12

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    With maybe 100M dwellings and 330M people in the U.S. this is not a big safety hazard. Vehicle deaths are about 30K per year and tobacco related deaths are ~500 per day.

    But, in any case, how has this changed from what the numbers were before AFCIs?

    You might be interested in reading
    http://www.amazon.com/unSpun-Finding-Facts-World-Disinformation/dp/1400065666
    Everybody talks about fact-checking but this book actually tells how to do it.

    And this book
    http://www.amazon.com/Risk-Practica...F8&qid=1392900657&sr=8-1&keywords=risk+ropeik
    really opened my eyes.
     
  13. Feb 20, 2014 #13

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,892
    Likes Received:
    3,117
    They are new in the grand picture, you will have to waite some time for the other half of those numbers.:)
     
  14. Feb 20, 2014 #14

    bud16415

    bud16415

    bud16415

    Fixer Upper Staff Member Admin Moderator

    Joined:
    Feb 5, 2013
    Messages:
    4,654
    Likes Received:
    1,597
    I find myself wanting to agree with Wuz here and on unfamiliar territory doing so. Sorry Wuz a bit of an attempt at humor.

    I tend to want to look at the big picture and the most bang for the buck as they say. Of course in a perfect world we would do everything in terms of safety all at once and adopt every new item as they come along but in the real world we have to do the best we can with what we have. I live in an area where we have lots of Amish and they believe in no electricity (except when they can use someone else’s) so they have gas lights and wood stoves and candles and lanterns. I don’t have the stats but from what I have seen they have zero deaths caused by arc faults per year in their homes, but have quite a few fire related ones from other causes. Point being some statistician could make a valid case for doing away with electricity pointing to the facts above.

    Dollar for dollar what would save more lives a smoke detector or an arc fault detector that I don’t know and of course both are better.

    I think Wuz’s point is there is always going to be arcing with switching and the device has to recognize an arc signature and determine good from bad. He being the inquisitive type wants to know what that signature is and no one is providing that information. I agree every life saved is worth it but at what cost. There is no end to safety measures only drawing a line at some level of acceptability. I have no idea about where that line is or how good these things work.

    I could make an analogy though suppose I determine that rodents eat thru wires and cause shorts and I have an annual death count from such. One method would be to install AFCI breakers another would be a method of rodent control. Statistically maybe I could prove getting rid of the rodents would over all save more lives from all rodent related causes, but electrical related deaths would show getting rid of rodents was only part of the arc related causes of death. Knowing the statistics is always good but also easy to use to prove something in one direction or the other. I have no clue what the big picture is on this issue but I do understand Wuz’s point on this one.
     
  15. Feb 20, 2014 #15

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,892
    Likes Received:
    3,117
    Wuzz may be right but the same questions come up with any new safety device.
     
  16. Feb 20, 2014 #16

    bud16415

    bud16415

    bud16415

    Fixer Upper Staff Member Admin Moderator

    Joined:
    Feb 5, 2013
    Messages:
    4,654
    Likes Received:
    1,597
    That’s what’s great about living in a free country, as much as we sometimes don’t agree we are allowed to debate and question. The process of doing that is a good one even when it is frustrating to one side of the debate. It forces the other side to be open and totally prove their side. Without such we have people that want to force an idea along to the finish line and sometimes call those that don’t agree “Members of the Flat Earth Society”. One of my biggest fears is the population is slowly dumbing down and becoming complacent to everything they are told. That never has ended well in history.
     
  17. Feb 20, 2014 #17

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    Someone mention fire?
    http://www.fireengineering.com/articles/2010/07/murphy-firefighter-arsonists.html

    Here's what may sell some of these gadgets
    "Humans have a zero-risk bias. This means we will opt for a small reduction in a risk to totally eliminate it rather than a larger reduction in a more significant risk. This is because we tend to choose more certain benefits (even if they are small) over larger, less uncertain benefits."
    from
    http://www.rmmagazine.com/2010/10/01/making-risk-assessments-useful/

    And this
    http://en.wikipedia.org/wiki/Fear,_uncertainty_and_doubt
     
    Last edited: Feb 20, 2014
  18. Feb 21, 2014 #18

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,892
    Likes Received:
    3,117
    Most people want to carry on with carrying on and then will change with new rules. But if someone they think they can trust says no way, they will want to go back to carrying on. Especially if the old way was cheaper. It works well for polititions, facts be dammed.
     
  19. Mar 31, 2014 #19

    92sb4x4oh

    92sb4x4oh

    92sb4x4oh

    Member

    Joined:
    Jan 15, 2012
    Messages:
    19
    Likes Received:
    0
    I would suggest that you might want to check your building codes to see what is required. I believe there is a code requirement that AFCI's be used in all bedrooms for code requirements. A good way to see which you should/can do would be to have a license electrician come in and give you an estimate on doing the work which would give you the how and why's of doing this to keep you family safe.
     
  20. Mar 31, 2014 #20

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    Try to get AFCIs that are made to the latest patents, probably with patent numbers like 6,000,000 and higher. These newer devices may be less sensitive to nearby radio transmitters and other things that cause false alarms and having to replace switches & motors before they are worn out.

    http://www.google.com/patents/US6414829

    Troubleshooting these things is pretty hard because they are go/nogo devices but Siemens makes a gadget to do this called Intelli-arc and there's a video on this. This thing tells you how close you are to tripping an AFCI and so you can find out why.
     
    Last edited: Mar 31, 2014