    I have a American Standard heat pump unit that will not switch from heat to cool.The thermostat has been replaced. The problem started after the house was struck by lightning. The switching valve will change over if either the orange or blue wire is unplugged. There is 24 volts at the control board and the LED is flashing normal.
     
  2. Mar 13, 2010 #2

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    is there 24Volts on the either the blue or orange.
    I'm thinking you have a short in one or both of them.
     
  3. Mar 13, 2010 #3

    proworker

    proworker

    proworker

    New Member

    Joined:
    Mar 13, 2010
    Messages:
    3
    Likes Received:
    0
    24 volts on both
     
  4. Mar 13, 2010 #4

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    I would think that you would have 24 volts on one or the other but not both. really sounds like a short in the control wire for the switching valve.
     
  5. Mar 13, 2010 #5

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    The most hardy components are things containing coils; solenoids, motors, relays.
    The least hardy are electronic components.

    I guess you should post a schematic.
    In your case it sounds like you can rig a bypass switch and so never have to solve the problem of finding the failed component(s).
     
    Last edited: Mar 13, 2010
  6. Mar 14, 2010 #6

    proworker

    proworker

    proworker

    New Member

    Joined:
    Mar 13, 2010
    Messages:
    3
    Likes Received:
    0
    sorry for the misinformation earlier. I have 24 volts on the orange wire not the blue. When I unplug either of them the valve switches. However I ohmed the ambient temp sensor and it is open, could this possibly be causing my problems?
     
  7. Mar 14, 2010 #7

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    Sorry, I don't have experience with heat pumps but, now that I think about it, you should have 24volts on both the switching valve and the A/C circuit.
    The blue is to run the A/C and the orange would reverse the A/C into heat mode. So yes, it could be the open ambient temp sensor holding out the voltage to the blue A/C wire. As a test, you could bypass the ambient sensor with a piece of wire and see if this allows the A/C to run.
     
  8. Mar 14, 2010 #8

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    Did you try both polarities when you checked it? Diodes can be used as temp. sensors but the wire colors into and out would be different.

    Usually the thermistor sensors read lower ohms when hot.
     
    Last edited: Mar 14, 2010