bad transformer?

Discussion in 'HVAC' started by randytrue, May 4, 2012.

  1. May 4, 2012 #1

    randytrue

    randytrue

    randytrue

    Member

    Joined:
    May 4, 2012
    Messages:
    5
    Likes Received:
    0
    During the winter, I noticed a loud hum coming from my furnace at all times.
    The other day, I tried to turn on the AC and got no response.
    Checked the furnace room, and found the noise is gone. No response at all from the thermostat, either heat or AC. Checked power, and there is power at the breaker.
    Should I start by replacing the 24V transformer?

    Randy
     
  2. May 4, 2012 #2

    Daddytron

    Daddytron

    Daddytron

    Well-Known Member

    Joined:
    Jan 29, 2012
    Messages:
    82
    Likes Received:
    4
    Megatron was a bad transformer...
    But on a serious note, I would check the output voltage on the transformer. What kind of furnace do you have?
     
  3. May 4, 2012 #3

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    Only replace components when they test bad.
    Could be the thermostat that is bad but, you would have to test that too.
    You will need a volt/ohm meter to perform most tests.
     
  4. May 5, 2012 #4

    randytrue

    randytrue

    randytrue

    Member

    Joined:
    May 4, 2012
    Messages:
    5
    Likes Received:
    0
    The furnace is a Janitrol AC30-10, SN 9412014 74
    I know my way around a VOM meter, so tell me what's next.

    Randy
     
  5. May 5, 2012 #5

    Blue Jay

    Blue Jay

    Blue Jay

    Well-Known Member

    Joined:
    Jun 6, 2008
    Messages:
    285
    Likes Received:
    25
    At the transformer check both the input and output side, should be 120V on input and 24V on the output. If that checks ok then check for 24V at the thermostat.
     
  6. May 5, 2012 #6

    randytrue

    randytrue

    randytrue

    Member

    Joined:
    May 4, 2012
    Messages:
    5
    Likes Received:
    0
    The thermostat is easier to check first.
    The most voltage I could find was 3V AC.

    Randy
     
  7. May 5, 2012 #7

    randytrue

    randytrue

    randytrue

    Member

    Joined:
    May 4, 2012
    Messages:
    5
    Likes Received:
    0
    Is there a component that will go out between the transformer input and the 120V?

    Randy
     
  8. May 5, 2012 #8

    randytrue

    randytrue

    randytrue

    Member

    Joined:
    May 4, 2012
    Messages:
    5
    Likes Received:
    0
    OK, I'm getting 13V AC at the transformer output.
    Can we assume the transformer is bad?

    Randy
     
  9. May 6, 2012 #9

    Blue Jay

    Blue Jay

    Blue Jay

    Well-Known Member

    Joined:
    Jun 6, 2008
    Messages:
    285
    Likes Received:
    25
    That would be my guess. Only thing that should be ahead of the transformer would be a switch or breaker.
     
  10. Sep 17, 2012 #10

    runfast

    runfast

    runfast

    heating expert

    Joined:
    May 7, 2010
    Messages:
    9
    Likes Received:
    0
    13v indicates the contactor on the a/c is partially shorted if the stat was calling for cooling.
     
  11. Sep 17, 2012 #11

    Rob-M

    Rob-M

    Rob-M

    Junior Member

    Joined:
    Sep 17, 2012
    Messages:
    1
    Likes Received:
    0
    If you have a 110v at the furnace then you have 110v into transformer, which is called the primary, test the secondary side of transformer (24v) by followingthe leads from transformer going to the low voltage connections usually "R" & "C" or "X" thats the 24v connections. Depending on well who has worked on your furnace and the manufacturer there maybe be a fuse once the 24v leaves the transformer going to the low voltage/thermostat connections may be a inline car fuse or colored fuse. If you have 24v there than you will at stat. On a call for cooling your stat will send 24v to the AC unit normally the yellow wire or "y" connection. Your 2 low voltage wires at AC unit are the 24v, so check the voltage there. Then it can go thru safety switches, circuit board then the contactor so follow it. Theres also manual resets at the AC unit to high and low pressure you may try resetting them. Can go on and on but its a start to save u a buck. Make sure your meter is on AC volts and not DC volts too. Good Luck

    Rob
     
  12. Sep 18, 2012 #12

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    A partial short should be pretty difficult to trace down without cutting and jumpering some connections on your controller board.

    Taking 40 VA as a generic rating for your transformer, the secondary current should be 40/24 = 1.7A or less. Check it if you can.
     