If the light is to be separate from the fan, I'd pick the NM with two conductors (blue jacket). This will be quick if it will reach the new light's location* (See the * notes in italic below)
Power the line side from your #7. Number six will be the neutral. (The fan will also use #'s 6 and 7)
Use the 3-conductor (white jacket) NM for the fan. This will make future diagnosis easier. And, you'll have an extra conductor at the fan should you ever decide to put a heater, night light or something else in the fan enclosure.
*Don't splice a jumper to the new light in the fan box's wiring enclosure unless your are certain the cubic inch capacity is sufficient for all of the wires.
It should be marked with cubic inch. Tell us the wire size and the cubic inch and Soonyb or I can do the math for you.
Usually, however they are sized only for a maximum of two #12, the grounds, the device wires and no internal clamping mechanisms.
*If you splice a jumper to reach the light in a separate box, be certain that the box is located where it will remain accessible. The attic is fine.
You can screw it to the top of the joist if you protect the wires leading to& from it with running boards. (Running boards aren't required if there are no stairs or permanent ladder and the cable is more than 6 feet from the opening to the attic.)
You can also mount the box to the side of the nearby joist and bore wiring holes to reach the new light location.
Soonyb mentioned the six inch of free conductor:
NFPA 70 Article 300.14 requires six inches of free conductor past the end of the raceway, cable or sheath.
If the box is less than 8" in any dimension (including depth) the wire has to be able to extend 3" past the edge of the box. (You'll be frustrated if you don't have a happy length of wire with which to work.)
Paul
Power the line side from your #7. Number six will be the neutral. (The fan will also use #'s 6 and 7)
Use the 3-conductor (white jacket) NM for the fan. This will make future diagnosis easier. And, you'll have an extra conductor at the fan should you ever decide to put a heater, night light or something else in the fan enclosure.
*Don't splice a jumper to the new light in the fan box's wiring enclosure unless your are certain the cubic inch capacity is sufficient for all of the wires.
It should be marked with cubic inch. Tell us the wire size and the cubic inch and Soonyb or I can do the math for you.
Usually, however they are sized only for a maximum of two #12, the grounds, the device wires and no internal clamping mechanisms.
*If you splice a jumper to reach the light in a separate box, be certain that the box is located where it will remain accessible. The attic is fine.
You can screw it to the top of the joist if you protect the wires leading to& from it with running boards. (Running boards aren't required if there are no stairs or permanent ladder and the cable is more than 6 feet from the opening to the attic.)
You can also mount the box to the side of the nearby joist and bore wiring holes to reach the new light location.
Soonyb mentioned the six inch of free conductor:
NFPA 70 Article 300.14 requires six inches of free conductor past the end of the raceway, cable or sheath.
If the box is less than 8" in any dimension (including depth) the wire has to be able to extend 3" past the edge of the box. (You'll be frustrated if you don't have a happy length of wire with which to work.)
Paul