    I have an outside breaker panel, located next to my meter, that contains breakers for my four outside A/C units and Pool Equipment. This panel also feeds two breaker panels located in the garage that contain all of the other breakers for the house. The garage panels are approx. 15-25ft of wire from the outside panel. Total is 400A - 200A for outside and 200A feeding garage panels. I'm considering the following Surge Protection Devices, which setup would you choose?

    #1 - Install Intermatic IG2240 SPD as a Type 1 device at the outside meter. This device has its own breaker switch and removable modules that can be replaced after they die. The specs are: In(kA) 10 - SCCR(kA) 10. PLUS install an Intermatic IG1240RC3 SPD as Type 2 on the garage breaker panel that has the downstairs circuits which include all of the kitchen appliances, most of the home computers, TVs etc. The specs on this SPD are: In(kA) 20 - SCCR(kA) 50

    #2 - Install 3 IG1240RC3s as Type 2 devices: The first would be on the breaker panel next to the meter on the bus that contains all of the breakers for the outside ACs etc. The top leg of this breaker panel that feeds the other garage breakers would not have very good protection at this point. Then I would install a 2nd and 3rd IG1240RC3 in the two garage breaker panels.

    (I only listed the In(kA) and SCCR(kA) specs because most of the other specs were identical)

    Thanks in advance for any advice you can provide :)

    Outside Panel.JPG
     
  2. Dec 19, 2017 #2

    hornetd

    hornetd

    hornetd

    Member

    Joined:
    Nov 18, 2005
    Messages:
    116
    Likes Received:
    75
    Surges Happen is a guide by the National Institute of Standards & Technology for protecting your electric and electronic devices from these electrical anomalies. It can be downloaded from https://www.nist.gov/document-18559. Once you have read it an followed the auditing process that it suggest then those with actual experience in the area of Surge and spike protection can help you with any questions that you might still have.
     
    afjes_2016 and OdeliaMurch like this.
  3. Jan 19, 2018 #3

    OdeliaMurch

    OdeliaMurch

    OdeliaMurch

    New Member

    Joined:
    Jan 17, 2018
    Messages:
    2
    Likes Received:
    0
    I would choose to install Type 2 IG1240RC3 SPD Surge Protection Devices, as it provides the highest ratings for the installation. It also eliminates the potentially hazardous failure modes that are commonly happening nowadays.
     
    Last edited: Jan 19, 2018
  4. Jan 19, 2018 #4

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,945
    Likes Received:
    3,131
    For a new member that looks a lot like spam. Oldog looks friendly but boy can he bite.:welcome:
     