Can I 3way cfls in series?

Discussion in 'Electrical and Wiring' started by garlandkr, Mar 8, 2013.

  1. Mar 8, 2013 #1

    garlandkr

    garlandkr

    garlandkr

    Member

    Joined:
    Oct 24, 2011
    Messages:
    22
    Likes Received:
    0
    I have this diagram I'm following, but the problem is that the lights flicker and if I remove one of them the others go out.

    3way_wiring.png
     
  2. Mar 8, 2013 #2

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    That is parallel wiring. ALL AC building wiring is parallel, regardless of the physical orientation of the lights and switches.
    Things like alarm systems are wired in series.

    You obviously wired them electrically in series, which is NOT good.
     
    drewdin likes this.
  3. Mar 9, 2013 #3

    drewdin

    drewdin

    drewdin

    Junior Member

    Joined:
    Aug 9, 2012
    Messages:
    440
    Likes Received:
    38
    I agree with speedy, if they were in parallel they wouldn't go out when you removed one.

    can you take some pictures of your setup? maybe the backs of the lights?
     
  4. Mar 9, 2013 #4

    Sparky723

    Sparky723

    Sparky723

    Member Sponsor

    Joined:
    Mar 9, 2013
    Messages:
    17
    Likes Received:
    2
    Are you telling him that's the only reason not to wire the cans in series? I can understand receptacles, but cans?
     
  5. Mar 9, 2013 #5

    wilard

    wilard

    wilard

    Member

    Joined:
    Feb 10, 2013
    Messages:
    9
    Likes Received:
    0
    It looks to me that the diagram is accurate. And you've wired it incorrectly

    You probably need another wire ran between the four lights .. Or depending on what's easier access
    Run a traveler directly between we the switches. Hard to tell since we don't know what you've done.
     
  6. Mar 9, 2013 #6

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    If we are to assume you are an electrician by your name, do you know the difference between series and parallel???
     
  7. Mar 9, 2013 #7

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,528
    Likes Received:
    273
    The drawing is correct. If removing one makes the others go out then you did not wire it like the drawing.
     
  8. Mar 9, 2013 #8

    garlandkr

    garlandkr

    garlandkr

    Member

    Joined:
    Oct 24, 2011
    Messages:
    22
    Likes Received:
    0
    Thanks for the replies everyone.

    This is an old house and I'm using existing wiring, the diagram was roughed out as a plan of action.

    Everything is working now. I had mixed up the black and white coming pff the last switch. Using a miltimeter I found which wire to use, the white was hot and the black wad neutral (old existing wire).
     
    Last edited: Mar 9, 2013
  9. Mar 12, 2013 #9

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,897
    Likes Received:
    3,118
    Thanks for the update.:)
     