    Hi,
    The fan on the outside unit, a Carrier 38EZA060310 Model, stopped turning yesterday. I took out the capacitor and got it tested and it was bad and replaced it. The unit worked fine for the afternoon while it was cooling the house. After it was off a while and came back on the fan wouldn't turn again. The compressor is coming on and we know the cap is good.
    My guess is bad fan motor. Can you verify?

    Thanks,

    Rick
     
  2. Jun 19, 2013 #2

    rstokes28

    rstokes28

    rstokes28

    Member

    Joined:
    Jun 19, 2013
    Messages:
    7
    Likes Received:
    0
    In addition to fan not turning unless I help it a little, when the system is one it's taking a long time to cool. Could this be an issue where it's been losing Puron steadily and has been stressing the components?
     
  3. Jun 19, 2013 #3

    Housedoctor57

    Housedoctor57

    Housedoctor57

    Active Member

    Joined:
    Mar 2, 2010
    Messages:
    40
    Likes Received:
    4
    If the fan motor is turning at a reduced RPM this will affect the unit's cooling ability. Also clean the coils with coil cleaner or a 409/Simple Green product. Wash out with a powerful stream of water from the garden hose. Be sure to set the thermostat to OFF and disconnect the power to the outside unit before you begin.
     
    rstokes28 likes this.
  4. Jun 19, 2013 #4

    rstokes28

    rstokes28

    rstokes28

    Member

    Joined:
    Jun 19, 2013
    Messages:
    7
    Likes Received:
    0
    Thanks Housedoctor57. I'm assuming along with the cleaning that the fan motor also e replaced, just to be sure.

    Best
     
  5. Jun 19, 2013 #5

    Housedoctor57

    Housedoctor57

    Housedoctor57

    Active Member

    Joined:
    Mar 2, 2010
    Messages:
    40
    Likes Received:
    4
    Yes, The fan should be replaced based on your description and the fact you exchanged the Cap already that helps with the start and run function of the motor. Good luck. Check your area for a Johnstone Supply location if you have trouble getting the part from another AC supply house.
     
    rstokes28 likes this.
  6. Jun 19, 2013 #6

    rstokes28

    rstokes28

    rstokes28

    Member

    Joined:
    Jun 19, 2013
    Messages:
    7
    Likes Received:
    0
    All cleaned up and now I'm hunting for the fan motor which I expect to be the end of this drama and back to some good AC in the Phoenix summer.

    Thank you for the good advice.
     
  7. Jun 20, 2013 #7

    rstokes28

    rstokes28

    rstokes28

    Member

    Joined:
    Jun 19, 2013
    Messages:
    7
    Likes Received:
    0
    I found a new fan motor with the same specifications for $111.00 and it got it installed with no problems. It came with its own capacitor which wasn't an issue. The home seems to be cooling at near double the rate it was before the failure.
    Thanks again for the help. -:)
     
  8. Jun 20, 2013 #8

    Housedoctor57

    Housedoctor57

    Housedoctor57

    Active Member

    Joined:
    Mar 2, 2010
    Messages:
    40
    Likes Received:
    4
    Good deal. You should have 18-21 degrees diff between the
    Cold air and return air temps once house stabilizes.
     
  9. Jun 20, 2013 #9

    rstokes28

    rstokes28

    rstokes28

    Member

    Joined:
    Jun 19, 2013
    Messages:
    7
    Likes Received:
    0
    What would be the best method and tool to check that difference?
     
  10. Jun 20, 2013 #10

    Housedoctor57

    Housedoctor57

    Housedoctor57

    Active Member

    Joined:
    Mar 2, 2010
    Messages:
    40
    Likes Received:
    4
    What I do is make a small hole in the duct above the A Coil that is connected to the furnace/air handler(assuming you have a vertical setup. If horizontal then insert between A Coil and duct work). Insert the thermometer there to check the air being cooled and also check the air at your filter in the return or make a small hole in the return duct and check right before it goes back into the air handler.
    I use a digital thermometer like this one. I buy mine locally at AC supply house. Use some foil tape or electrical take to cover the tiny hole you made in the ducts.

    http://www.amazon.com/Taylor-Digita...50&sr=8-26&keywords=probe+digital+thermometer
     
  11. Jun 20, 2013 #11

    rstokes28

    rstokes28

    rstokes28

    Member

    Joined:
    Jun 19, 2013
    Messages:
    7
    Likes Received:
    0
    Great. I'll try this. Had a good cool night last night in the Phoenix heat and everything is working well.

    Thanks!
     