Cold air coming through eletrical outlets.

Discussion in 'Insulation and Radiant Barriers' started by swimmer_spe, Jan 18, 2018.

Help Support House Repair Talk by donating using the link above.
  1. Jan 18, 2018 #1

    swimmer_spe

    swimmer_spe

    swimmer_spe

    Well-Known Member

    Joined:
    Apr 29, 2015
    Messages:
    418
    Likes Received:
    82
    In my kitchen I noticed a draft. It was coming from a wall outlet on an exterior wall.
    Are there simple solutions for this, or an I going to have to rip the drywall apart?
     
  2. Jan 18, 2018 #2

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,986
    Likes Received:
    3,149
    Sparky617 likes this.
  3. Jan 18, 2018 #3

    swimmer_spe

    swimmer_spe

    swimmer_spe

    Well-Known Member

    Joined:
    Apr 29, 2015
    Messages:
    418
    Likes Received:
    82
  4. Jan 18, 2018 #4

    bud16415

    bud16415

    bud16415

    Fixer Upper Staff Member Admin Moderator

    Joined:
    Feb 5, 2013
    Messages:
    4,721
    Likes Received:
    1,628
    I would try some great stuff spray foam before I ripped the wall apart. take off the outlet cover and see if there is a big gap around the Jbox where air is blowing in.

    It is not the best fix because air / wind is getting in some place but in the middle of the winter it will seal it up I would think.
     
  5. Jan 18, 2018 #5

    bud16415

    bud16415

    bud16415

    Fixer Upper Staff Member Admin Moderator

    Joined:
    Feb 5, 2013
    Messages:
    4,721
    Likes Received:
    1,628
    Neal's idea looks good as well. Try them first.
     
    Sparky617 likes this.
  6. Jan 18, 2018 #6

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,986
    Likes Received:
    3,149
    You didn't I was thinking about it.
     
  7. Jan 18, 2018 #7

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,986
    Likes Received:
    3,149
    swimmer_spe likes this.
  8. Feb 19, 2018 #8

    swimmer_spe

    swimmer_spe

    swimmer_spe

    Well-Known Member

    Joined:
    Apr 29, 2015
    Messages:
    418
    Likes Received:
    82
    So, I removed the cover on the outlet. It has one of those foam things for it. I am replacing it with a new one.

    Without tearing apart the wall, is there any safe option to insulate the box?
     
  9. Feb 19, 2018 #9

    bud16415

    bud16415

    bud16415

    Fixer Upper Staff Member Admin Moderator

    Joined:
    Feb 5, 2013
    Messages:
    4,721
    Likes Received:
    1,628
    #4 ............
     
  10. Feb 19, 2018 #10

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,986
    Likes Received:
    3,149
    I doubt if there is a fix for it with much less that a vapour barrier.

    Air is sucked into a house as it is needed to replace fire air and bath fan and people.
    Do you have fresh air intake near the furnace?
    When the pressure is higher inside, the warm air will leak out. That is worse as that warm air has moisture in it that will condense in the walls.
     
  11. Feb 19, 2018 #11

    swimmer_spe

    swimmer_spe

    swimmer_spe

    Well-Known Member

    Joined:
    Apr 29, 2015
    Messages:
    418
    Likes Received:
    82
    The only gap I see without removing the outlet is simply the space in the box. There is no gap of drywall.
     
  12. Feb 19, 2018 #12

    swimmer_spe

    swimmer_spe

    swimmer_spe

    Well-Known Member

    Joined:
    Apr 29, 2015
    Messages:
    418
    Likes Received:
    82
    There are 2 pipes from outside directly plumbed to my furnace. One is intake, one is exhaust.
     
  13. Feb 19, 2018 #13

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,986
    Likes Received:
    3,149
    So that is fire air. You don't have replacement air for all the other stuff.
    It has to come from somewhere. If you crack a window open a touch somewhere in the house will the draft change? We used to see air run right into the return air, I think that would allow the house to pressure up and cause mold at all the leaks.
     
  14. Feb 19, 2018 #14

    swimmer_spe

    swimmer_spe

    swimmer_spe

    Well-Known Member

    Joined:
    Apr 29, 2015
    Messages:
    418
    Likes Received:
    82
    My cold air return for the duct work is in my living room, about 20 feet away.
     
  15. Feb 19, 2018 #15

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,986
    Likes Received:
    3,149
    Yeah, they used to run an outside air intake into the return air. Then you would be pushing warm air out those leaks I think you best bet is to have fresh air coming in somewhere so the pressure difference inside to outside is neutral. If testing that with an open window proves that the drafts decreases then you could add a fresh air vent somewhere.
     
  16. Feb 19, 2018 #16

    joecaption

    joecaption

    joecaption

    Well-Known Member

    Joined:
    Jan 8, 2011
    Messages:
    2,088
    Likes Received:
    305
    Most common cause is the attic and or crawl space have not been air sealed.
    The wires to supply the power is ran through the top or bottom plates inside the wall.
    If the holes have never been sealed with expanding foam cold air can get in.
     
    nealtw likes this.