Delayed ac startup

Discussion in 'HVAC' started by JALEXED2, Jul 13, 2009.

  1. Jul 13, 2009 #1

    JALEXED2

    JALEXED2

    JALEXED2

    Member

    Joined:
    Jul 10, 2009
    Messages:
    20
    Likes Received:
    0
    My ac does not startup for about 15 minutes after requesting ac at the thermostat. Fan switch is on auto, switch is on cool, and temperature slider switch is down around 60 degrees when the house is about 80. Sometimes the ac starts right up as i would expect. Sometimes it delays about 15 minutes.

    Do i have a thermostat on the way out?
     
  2. Jul 13, 2009 #2

    CraigFL

    CraigFL

    CraigFL

    Well-Known Member

    Joined:
    Mar 13, 2006
    Messages:
    409
    Likes Received:
    0
    You need to determine where the problem is. Does the compressor outside start right away? Does the outside fan start right away? If it is the thermostat, you should be able to jumper two wires behind the thermostat to start the compressor right away...
     
  3. Jul 16, 2009 #3

    onecrazyfoo4u

    onecrazyfoo4u

    onecrazyfoo4u

    Member

    Joined:
    Jul 7, 2009
    Messages:
    15
    Likes Received:
    0
    Also be aware that most modern day thermo's have a delayed startup for about 5 minutes when the A/c has just been shut off.
     
  4. Aug 1, 2009 #4

    JALEXED2

    JALEXED2

    JALEXED2

    Member

    Joined:
    Jul 10, 2009
    Messages:
    20
    Likes Received:
    0
    I checked the wiring and all was fine. I replaced the thermostat with a 5/2 programmable thermostat and everything seems fine. My orginal thermostat was the mercury bubble tube type so I didn't mind the upgrade. $15 bucks on E-bay. Thanks for your comments!
     