    Thanks for all the great information. I have learned so much from everyone. One thing I learned is that my main electrical panel is a mess. I wanted to add a new breaker so I opened the panel and found numerous spots where the ground and nuetral wires are under the same screw. From what I can tell they are not part of the same circuit. I don't know if that makes a difference. My question is, should I clean these bus bars up. Should I remove all the wires and place the nuetrals under single screws and possibly triple the grounds so I have enough room for the new breaker. Can I add a new bus bar? If so, how?

    I went back to look at my original home inspection to see if this was missed. The inspector passed it because none of the hots were double wired and the nuetral and grounds were not wired together in a sub panel. Is this correct.

    Thanks so much!!
     
  2. Sep 12, 2011 #2

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    The main panel will have ground and neutral sharing the same bar.
    The sub panle will have the ground and neutral separate.
    You can double the ground or neutral in either panel as long as you observe the rules previously stated.
     
  3. Sep 13, 2011 #3

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,528
    Likes Received:
    273
    You can not double the neutral in main or sub panel. One neutral wire per terminal.
     
  4. Sep 13, 2011 #4

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    +1 :agree:
     