GFCI humming sound when pressed

Discussion in 'Electrical and Wiring' started by th112358, Apr 5, 2009.

  1. Apr 5, 2009 #1

    th112358

    th112358

    th112358

    New Member

    Joined:
    Apr 5, 2009
    Messages:
    1
    Likes Received:
    0
    I have read almost all the threads relating to GFCI and would like to post to ask you all to help.

    My Septic seemed to have no power (Pump not running). One GFCI inside the house gave a humming sound when pressed and won't reset (All other ones tested ok).

    I flipped all the circuit breakers and they seems to be functioning.

    What else can I do? Please help and TIA.
     
  2. Apr 5, 2009 #2

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    remove the wires from the LOAD terminals on the GFI before attempting to reset it.
    If it resets, then you have a problem downstream of the GFI.
    If it still fails to reset, replace the GFI.
     
  3. Apr 5, 2009 #3

    glennjanie

    glennjanie

    glennjanie

    Well-Known Member

    Joined:
    Mar 1, 2006
    Messages:
    2,990
    Likes Received:
    4
    Welcome TH:
    It sounds like this circut may feed a sewage pump in the septic tank for a 'mound system'. If that is the case, you could open the tank with the pump and make sure the wire to the pump hasn't been damaged in some way. The pump should also have a rope attached to pull it out with.
    You should be able to pull the pump out and plug it into another receptacle to make sure it isn't frozen or siezed.
    Glenn
     
  4. Apr 14, 2009 #4

    triple D

    triple D

    triple D

    Well-Known Member

    Joined:
    Jan 30, 2008
    Messages:
    296
    Likes Received:
    1
    If you pull your pump and plug into a cord direct, make sure you point the damn outlet clean away. I learnt this one the hard way. Good luck...
     