Ground rod

House Repair Talk

Help Support House Repair Talk:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

trigg

Active Member
Joined
Nov 4, 2012
Messages
28
Reaction score
1
Hi
I will have to be installing a 8ft ground rod to meter box an wanted to know some of the basics on it .-

Is it required to be in condoit?

And can the bare copper be in same conduit as main feed wires going from meter box to panel?

An am i to have 2 rods?

Is it best to be as close to meter as possible an have the bare copper wire enter lower side of meter box or is it to go into bottom?

Also can it be joined to same lug [neutral feed after meter has a side lug bolted to box off neutral.], inside meter box, as the bare copper wire from panel ground will be ?
Can water pipe be used as 2nd ground source ,an would i go from rod to pipe?

Any other important things i need to know please do share.
Thanks
 
It sounds like you are, installing/having installed, a sub-panel as opposed to a main service, so you need to better state your case, because the rules are different.
 
No
Im required to ground the meter box an panel
.neither are grounded
 
OLD Meter box has nothing but the 3 main in /3 main out
 

Attachments

  • 20180618_072436.jpg
    20180618_072436.jpg
    50.4 KB · Views: 10
Please answer what i asked on requirements .
Is it required to use the condoit?

An have 2nd grounding point after rod?

Is it required that rod be so far from panel an meter?

Etc,list
 
So, the meter encl. is not grounded, and the disassociated service distribution panel also is not grounded and you are required, by somebody, to provide service equipment grounding before the utility will provide a service drop?
 
They wont reconnect service till its done.
So it WILL BE INSPECTED .

Id like to use this double lug for both #4 coppers in meter box to the neutral lug,on far right in pic,but unsure poco will approve.

I want to be sure i cover it all including ground rod requirements .
 

Attachments

  • P16055.jpg
    P16055.jpg
    21.6 KB · Views: 4
Last edited:
Please answer what i asked on requirements .
Is it required to use the condoit?

An have 2nd grounding point after rod?

Is it required that rod be so far from panel an meter?

Etc,list

I'm attempting to draw a mental picture of your situation so that the members can constructively off you appropriate answers.

The driven ground rod encased in a conduit is simply a rod within a rod and has nu use other than taking up space. therefore the rod must be encased in the earth or by virtue of another metallic conductor encased in concrete buried in the ground.

Having a 2nd ground rod is recommended for services of 200amps, placed 7' apart.

The placement of the ground rod becomes a mater of convenience, IE, it is more convenient to have the ground rod next to or in the general proximity of a metallic plumbed hose bib, fewer clamps less opportunity for disassembly.
 
Is the lug on far right not the location for ground ?
It meets under neutral .

An what are those round oval cone like shaped pieces poking out on both sides from middle of meter..right one has tan covering over black part of it.
 

Attachments

  • 20180618_072330.jpg
    20180618_072330.jpg
    65 KB · Views: 20
  • 20180618_200146.jpg
    20180618_200146.jpg
    33.3 KB · Views: 19
  • 20180618_072436.jpg
    20180618_072436.jpg
    50.4 KB · Views: 15
Last edited:
Hi
I will have to be installing a 8ft ground rod to meter box an wanted to know some of the basics on it .-

Is it required to be in condoit?

And can the bare copper be in same conduit as main feed wires going from meter box to panel?

An am i to have 2 rods?

Is it best to be as close to meter as possible an have the bare copper wire enter lower side of meter box or is it to go into bottom?

Also can it be joined to same lug [neutral feed after meter has a side lug bolted to box off neutral.], inside meter box, as the bare copper wire from panel ground will be ?
Can water pipe be used as 2nd ground source ,an would i go from rod to pipe?

Any other important things i need to know please do share.
Thanks
Let me take your questions in the order you asked them:

You are allowed to use #6 American Wire Gauge (6AWG) as the Grounding Electrode Conductor (GEC) when connecting to Driven Rod Electrodes. If you use 6AWG and it is exposed to physical damage; such as adjacent to a walkway, or similar exposure you must protect it from damage by Enclosing it in Rigid Metal Conduit or Schedule 80 Rigid Non Metallic Conduit. It must be protected all the way to the connection to the rod or to a depth of 2 feet. The way to avoid that is to use #4 AWG Copper (CU) as the GEC because #4 and larger conductors are only required to be protected when exposed to severe physical damage. One examples of such exposure include grass that goes right up to the GEC making exposure to powered lawn equipment nearly inevitable. Another would be installation immediately adjacent to a driveway. In such cases even conductors as large as #4 AWG would require protection. Removing the sod and replacing it with a one foot or wider strip of mulch were the GEC enters the earth will satisfy most Authorities Having Jurisdiction (AHJ); read electrical inspectors; that the GEC is not exposed to powered landscaping equipment.

There is no reason to have an additional conductor in the raceway containing the Service Entry Conductors. The connection provided in the Meter Enclosure; meter can; is enough to connect the portion of the Grounding Electrode System to the Grounded Current Carrying Conductor; neutral.

As to the number of Driven Rod Electrodes (ground rods) you must have it can be a single rod if it has an impedance to ground of 25 Ohms or less. If the impedance of the single rod is more than 25 Ohms you will need to drive a second rod at least 6 feet away from the first rod. Since the equipment to test that impedance is quite expensive most installers simply install the second rod. The National Electrical Code allows the first rod to be driven right next to the wall on which the meter is mounted but that is well short of best practice.

The GEC should enter the meter can through a knock out in the bottom of the enclosure. Look carefully and you will find a knock out almost immediately below the GEC lug in the bottom of meter can in the case of most manufacturers' enclosures.

Best practice is to drive the ground rods into an area of soil, that has a radius around the rod which is the length of the rod itself and which is free of any underground structures including the basement wall or foundation of the home. That would mean that you would drive an 8 foot rod at least 8 feet out from the basement wall or foundation. Best practice is to drive the second rod at least twice the length of the longest rod away from the first. For two 8 foot rods that would be sixteen feet apart.

A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing bonded to the pipe) must be connected to the Main Bonding Jumper using a terminal that is attached to the Neutral Buss in the Service Equipment Enclosure. So not only may you use it, you are required to use it as part of the Grounding Electrode System (GES) if it is available. It must be connected using a #4 AWG or larger CU conductor. The connection to the underground metal water pipe has to be made within 5 feet of were that piping enters the home. Pest practice is to make that connection on the supply side of the first shut off valve. That is because no one is likely to disturb piping that they cannot shut off. As long as that GEC is run inside the house it is unlikely to require physical protection. If for some good reason you were connecting from the driven rods to the underground metal water piping the GEC connecting the rods to the meter can's lug would have to be sized to the code requirement for the GEC to the water piping rather than the size required for the driven rods. That is so that it would be large enough to serve as the connection to the water piping via the driven rods. If instead you connected from the Service Equipment Enclosure's neutral buss to the water piping and then from the water piping to the driven rod electrodes the GEC from the pipe to the driven rods would only need to be sized to that required for driven rods which is #6 AWG.



If the water piping supplying water to the home is non metallic or less than 10 feet in length then you only need to bond the neutral to any metal water piping inside the home. That connection can be made at any convenient point on the interior metallic piping system.

--
Tom Horne
 
Thanks .
I found out that the #4 bare copper at meter base area goes to the weatherhead an joins the neutral up there.
I ran that wire to left lug in meter box.pic has lug on left before wire from weatherhead is in .
I ran bare #4 from ground rod to the neutral bar in meter box.
Does this look like it will pass,once i run that 2nd wire to left lug?
I used grey pvc also.pics are before i ran left #4 an secured pvc
And how far away is Ground rod to be ?
Thanks
 

Attachments

  • 20180627_203738.jpg
    20180627_203738.jpg
    56.4 KB · Views: 18
  • 20180629_095153.jpg
    20180629_095153.jpg
    21.1 KB · Views: 13
Last edited:
There is something wrong here. I think that you are misinterpreting something that you have read or been told. Where does the conductor which is connected to the Right most lug in the meter enclosure connect to? Is the conductor which is attached to the Grounded Service Entrance Conductor at the Service Entrance Raceway head connected to that same conductor at both ends?

Grounding Electrode Conductors connect the Grounded Service Entry Conductor to a Grounding Electrode. If the conductor does not have one end connected to a Grounding Electrode it is not a Grounding Electrode Conductor. It is true that the connection of the Grounding Electrode Conductor to the Grounded Service Entry Conductor; or neutral; can be made anywhere between the connection point of the Service Entry Conductors to the Service Drop and the Main Bonding Jumper in the Service Equipment Enclosure. That said I have never seen the Grounding Electrode Conductor run inside a service raceway. The conductor in your photographs appears to run in parallel with the Grounded Service Entry Conductor and thus serves no useful purpose at all.

Do you have a copy of the Service Standard for residential services from your local power utility? The only connections which are routinely made in the meter enclosure are the connections between the Service Entry Conductors and the Meter Base and the connection between the Grounded Service Entry Conductor and the Grounding Electrode Conductor.

What is the purpose of the PVC conduit connector that is shown on the left side in the interior photograph of the meter enclosure. Please back out and provide a picture of the meter enclosure which shows were every conductor that terminates in the enclosure goes.
 
The electrical company noted on #4 copper thar came from weatherhead that it needed to be grounded, an also that meter box needed to be grounded to ground rod ..
The meter was NOT grounded.
Schedule 40 for electric Ground entrance to meter is required here.
Ive talked w 3 local electricians here an on poco requirements here also..
 
Last edited:
Trigg

Where is the "#4 copper thar came from weatherhead" Grounded? Why does it enter the Weatherhead? Can you take the picture that I asked for? What is the purpose of the Non-Metallic conduit connector that enters through the left side of the meter enclosure? Where does the bare wire which is connected to the right hand most threaded post go after it leaves the bottom of the Meter Enclosure? Without the answers to those questions I will not be able to help.

--
Tom Horne
 
Trigg

Where is the "#4 copper thar came from weatherhead" Grounded? Why does it enter the Weatherhead? Can you take the picture that I asked for? What is the purpose of the Non-Metallic conduit connector that enters through the left side of the meter enclosure? Where does the bare wire which is connected to the right hand most threaded post go after it leaves the bottom of the Meter Enclosure? Without the answers to those questions I will not be able to help.

--
Tom Horne
 

Attachments

  • 20180629_095158(0).jpg
    20180629_095158(0).jpg
    20.4 KB · Views: 6
In pic the #4 bare runs up to weatherhead an is tied into the Neutral as its comes in before entering thru weatherhead.
The other end ends at meter base--it was just hanging when poco was there!It was pushed in behind meter non attatched.

Cant leave it hanging of coarse.
It will be terminated in meter box .
Left side.

They also said to add ground rod for meter to be grounded.
Thats where the copper is from bottom of meter ,from Ground rod to neutral bar .
 