    I am planning on installing a new 200 amp panel in my home in a different location than the existing panel that will be eliminated.
    I am adding on a new addition and have been told the rebar must be grounded. How is this done ? What size ground wire ? Should the clamp to the rebar be encased in the footing or exposed ? Is a ground rod also needed is so how long and how far away from the rebar ground ?
     
  2. Oct 16, 2009 #2

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,528
    Likes Received:
    273
    It's called a UFER ground.
     
  3. Oct 16, 2009 #3

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    Ufer is our name for a "concrete encased electrode". Sort of like "Band Aid".

    The connection must us an approved rebar connector.
    It can be in the pour or exposed.
    You need #4cu for your 200A service.

    NO, no other additional electrodes are required to be installed. If you have a metallic water line feeding the house you must use this as an electrode also.
     
  4. Oct 17, 2009 #4

    Dan K

    Dan K

    Dan K

    Member

    Joined:
    Oct 15, 2009
    Messages:
    6
    Likes Received:
    0
    Thanks for the feedback, I need to get a temporary service going and want it prepped right for the permanent setup as well.
     