Heat Pump - Aux stuck on.

Discussion in 'HVAC' started by pholt80, Oct 31, 2012.

  1. Oct 31, 2012 #1

    pholt80

    pholt80

    pholt80

    New Member

    Joined:
    Oct 30, 2012
    Messages:
    2
    Likes Received:
    0
    I have an electric heat pump and when you turn the thermostat on to heat, the aux heat comes on immediately and the air handler will not shut off even after the set temperature is reached. It just keeps blowing hot air with the aux heat on. The heat pump cycles like it should but the air handler will not. When the thermostat is on cool, everything works fine. The air comes off and on like it should. Should I suspect a sequencer on the heat circuit?
     
  2. Nov 6, 2012 #2

    americool

    americool

    americool

    New Member

    Joined:
    Nov 6, 2012
    Messages:
    2
    Likes Received:
    0
    It doesn't sound like a sequencer problem if the sequencer was stuck the heat strips would run with the a/c. Have you checked to see if that's the case? Sounds like a thermostat problem either bad or not setup properly in the internal installers menu
     
  3. Nov 6, 2012 #3

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,897
    Likes Received:
    3,118
    Hay look! two new people.:welcome:
     
  4. Nov 7, 2012 #4

    americool

    americool

    americool

    New Member

    Joined:
    Nov 6, 2012
    Messages:
    2
    Likes Received:
    0
    Thanks, looks like a great place to help DIY's and get feedback on problems.
     
  5. Nov 7, 2012 #5

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
  6. Nov 13, 2012 #6

    pholt80

    pholt80

    pholt80

    New Member

    Joined:
    Oct 30, 2012
    Messages:
    2
    Likes Received:
    0
    I bought a new thermostat and still have the same issue. Changed out the sequencer as well, still have the problem. I traced the wires from the thermostat to the furnace and did not find any problems. Any ideas?
     
  7. Nov 13, 2012 #7

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    Post the entire schematic in legible chunks and get out your multimeter.
     