insulate over old knob-and-tube wiring?

Discussion in 'Electrical and Wiring' started by Bru, Nov 2, 2010.

  1. Nov 2, 2010 #1

    Bru

    Bru

    Bru

    New Member

    Joined:
    Jun 27, 2009
    Messages:
    3
    Likes Received:
    0
    Mates:
    I'm in a house built in the '20s, which still has a few circuits on the old 2-wire knob & tube wiring, some of which runs across the floor joists in the attic. I really need to add a foot or so of fibreglas insulation to the attic, but am not in a position presently to rewiire the old circuits.
    Is there any danger to putting the fibreglas insulation batts over the top of the old wiring?
    Thanks for any suggestions or info.
    Bru
     
  2. Nov 2, 2010 #2

    paul52446m

    paul52446m

    paul52446m

    Well-Known Member

    Joined:
    Oct 7, 2010
    Messages:
    435
    Likes Received:
    1
    I don't think i would do that. The more amps that you run through a wire, the hotter the wire gets. So if you have the insulation around these old wires that can get very hot. The covering on the wires is already old, cracked, and if you heat it up a lot more the coating will really get bad.
    I would rewire before insulation. The air around the wires is what cools them. Later Paul
     
  3. Nov 2, 2010 #3

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,524
    Likes Received:
    272
    K&T is meant to be an open air system for cooling purposes. You are not supposed to bury it in insulation.
     
  4. Nov 2, 2010 #4

    Bru

    Bru

    Bru

    New Member

    Joined:
    Jun 27, 2009
    Messages:
    3
    Likes Received:
    0
    Thanks, guys. Sure am glad I asked. Looks like there's an electrician in my future.
    Bru
     
  5. Nov 3, 2010 #5

    Redbirdseven

    Redbirdseven

    Redbirdseven

    Member

    Joined:
    May 27, 2009
    Messages:
    8
    Likes Received:
    0
    I will just jump in here and agree with Paul and Joe .. Never cover K&T just to risky to take that chance.
     
  6. Nov 7, 2010 #6

    BBrown

    BBrown

    BBrown

    New Member

    Joined:
    Jul 6, 2009
    Messages:
    3
    Likes Received:
    0
    I have uncovered knob and tube wiring with scorch marks inside the cavities. They are simply undersized for today's loads. Personally, if I can see it, I replace it.
    Bob
     
  7. Nov 7, 2010 #7

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    This is not exactly accurate. It is not that the wire is undersized, more often they are over-fused by people removing or replacing 15's and 20's with 30's.
     