Background: Built a basement closet which contains my (2) FPE 200 amp service boxes. I just mounted a T8 Two strip fluorescent light on the ceiling controlled by a single pole switch. All wires are ran... Question: I have a leftover 20 Amp breaker available (American Single pole HARC type), is this too big for this single light circuit? I have numerous open slots for new circuits. If so, I don't want to buy a 15 Amp breaker due to big $$'s, so should I just tap into an existing 15 Amp circuit? Thanks for your responses, Todd
No. The breaker protects the circuit wire, not the fixture. I would. I see NO reason whatsoever for running a new 20A circuit to install one fluorescent light.
Thanks for the reply. My real concern is using a 20 Amp breaker for a light only circuit (which is usually 15 AMP) and posing a greater possible fire hazard. So, if I opted for the 20 AMP breaker (easier), does anyone foresee any issues? thanks, todd
If the circuit is wired with #12 wire then you can use the 20 amp breaker. If it is wired with #14 then you must use a 15 amp breaker.
Glad it works for you. Now you have plenty of room to add several other lights on same circuit in future.