Luxaire 4 red flashes error

Discussion in 'HVAC' started by musicis, Nov 12, 2008.

  1. Nov 12, 2008 #1
    Hello....I fired up my ~ 10 year old furnace just today for the first time this cold season and got consistent cold air blowing out the vents. The control panel is flashing 4 times and then a pause. I found a pdf form that says this about the error message:

    "4 RED FLASHES: This indicates that a primary or auxiliary limit switch has opened its normally closed contacts. The control will operate the supply air blower and inducer. This condition may be caused by: dirty filter, improperly sized duct system, incorrect blower speed setting, incorrect firing rate or faulty blower motor. Also, this fault code could be caused by a blown fuse located on the control board."

    I checked the fuse and its good. I checked the Primary and auxiliary contacts with no power on the furnace and continuity was there. I assume the contact breaks when the system starts? Filter is new. Blower seems good. Any help on this would be great. Model g8t08012dna11a serial wdlm003595

    Thanks in advance for any help.
     
  2. Nov 12, 2008 #2

    glennjanie

    glennjanie

    glennjanie

    Well-Known Member

    Joined:
    Mar 1, 2006
    Messages:
    2,990
    Likes Received:
    4
    Welcome Musicis:
    It appears you have covered most of the trouble-shooting items. We know it has worked for 10 years with the duct, blower speed, same blower motor and firing rate. Now, we must decide which of these items has changed; check for obstructions in the duct, or too many registers blocked or turned off, we don't have a firing rate because we are blowing cold air.
    It may help to do some cleaning on the furnace. Spiders love to build little nests in the pilot tube, the openings of the burners and other places. If it is a standing pilot, is it burning? or is the hot surface ignitor heating up? Do the burners come on at all? If it is a standing pilot, I would check the thermocouple.
    We are still open to further information or questions, and please let us know how it works out for you.
    Glenn
     
  3. Nov 12, 2008 #3

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    replace the bad limit switch.
     