    I finally got meter grounded an wanted to get the opinions of many before i talk w poco for power to be back on.
    There was a prexisting #4 copper off weatherhead neutral that i grounded to panel on left side ,already there.
    And a new#4 copper from ground rod to bottom of panel then lug at neutral bar.
    I also ran conduit but not shown in pic

    Also what was purpose of a #4 to neutral then meter off weather head entrance?

    Any info before inspected is appreciated
     

    Attached Files:

  2. Jul 2, 2018 #2

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,572
    Likes Received:
    284
    I have never heard of or seen a ground wire going up to the weatherhead.
     
  3. Jul 3, 2018 #3

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    24,146
    Likes Received:
    3,187
    What would happen if you did have a short to ground there?
    But would it not be grounded if the mast was attached to the meter box?
     
  4. Jul 3, 2018 #4

    Snoonyb

    Snoonyb

    Snoonyb

    Well-Known Member

    Joined:
    Sep 30, 2006
    Messages:
    3,208
    Likes Received:
    568
    The 3 utility conductors, and the cable tied to the service mast are call a service drop.

    Here on the truly left, nanny state, coast there is a ground conductor on the pole which is tied to the cable anchoring the service drop to the service mast, the service is them grounded to a driven ground rod.

    In over 40yrs, i've never seen the neutral from the service drop tied directly to ground.

    I'd ask the utility to have a look, as a courtesy, before you call for service.
     
    nealtw likes this.
  5. Jul 8, 2018 #5

    trigg

    trigg

    trigg

    Active Member

    Joined:
    Nov 5, 2012
    Messages:
    26
    Likes Received:
    1
    20180708_133144.jpg 20180705_131025.jpg 20180702_125331.jpg Got Approved!
    Tech said its double bonded at meter,


    Even with that #4 terminated in meter ,on left, box so i guess its not a factor terminated in box vs terminated to ground Rod

    Yes many old homes had this set up w neutral wire feed .They never upgraded .
     