Natural Gas Furnace - no heat

Discussion in 'HVAC' started by madrussian, Dec 20, 2016.

  1. Dec 22, 2016 #21

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,895
    Likes Received:
    3,117
    That could be a problem.:)
     
  2. Dec 22, 2016 #22

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    Check around on the transformer. Sometimes they have a manual overload reset button on them.
    Leave your meter on the hsi wires or at board during ignition and see if it ever gets that far.
    Are you still showing 3 blinks?
     
  3. Dec 22, 2016 #23

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    If you do replace the transformer put an inline fuse on the secondary.
    Short in the system may have burned it up.
     
  4. Dec 24, 2016 #24

    Jeffh

    Jeffh

    Jeffh

    Member

    Joined:
    May 23, 2014
    Messages:
    19
    Likes Received:
    4
    Does the hsi glow red hot during the operation? That should happen next. Then, gas valve clicks open, flame sensor keeps gas valve open, low limit initializes, blower kicks on...
     
  5. Dec 26, 2016 #25

    madrussian

    madrussian

    madrussian

    Member

    Joined:
    Dec 20, 2016
    Messages:
    15
    Likes Received:
    4
    It was the transformer. As soon as it was replaced, turned the system on, the HSI got red hot and gas flowed.
     
    oldognewtrick and nealtw like this.
  6. Dec 26, 2016 #26

    oldognewtrick

    oldognewtrick

    oldognewtrick

    Administrator Staff Member Admin Moderator

    Joined:
    Jul 26, 2009
    Messages:
    10,818
    Likes Received:
    1,434
    We love happy endings.
     
  7. Dec 27, 2016 #27

    madrussian

    madrussian

    madrussian

    Member

    Joined:
    Dec 20, 2016
    Messages:
    15
    Likes Received:
    4
    I actually stumbled across the fix. When schematic was reading 24V, I was measuring in DC, not AC. Doh.

    the flow chart led me to replace the xformer but I dont think it was the 24v side, I think the 120V side wasn't completely operational.
     
  8. Dec 27, 2016 #28

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,895
    Likes Received:
    3,117
    You must of had 120 volts on that side and that is really all you can check on that side. After that anything that prevents you from getting 24 volts is the problem with the transformer.
     