no AC in July, what fun

Discussion in 'HVAC' started by rheemed, Jul 14, 2009.

  1. Jul 14, 2009 #1

    rheemed

    rheemed

    rheemed

    Member

    Joined:
    Jul 14, 2009
    Messages:
    5
    Likes Received:
    0
    it's a rheem heat pump, copeland scroll compressor

    had an issue two weeks ago, seemed to be worn contactor, replaced it, things seemed ok for a couple of days

    next replaced thermostat, old mercury switch type for digital, again seemed to have helped but compressor just worked inconsistantly

    tonight it just will not stay on, it's almost midnight and it's hot

    checked stuff with voltmeter as some other threads suggested, but can't
    make sense of it

    what readings should be where?

    any help appreciated:confused:
     
  2. Jul 14, 2009 #2

    rheemed

    rheemed

    rheemed

    Member

    Joined:
    Jul 14, 2009
    Messages:
    5
    Likes Received:
    0
    couldn't find 24V anywhere, 18-19V at a few spots and 4-5V at others

    transformer?
     
  3. Jul 14, 2009 #3

    rheemed

    rheemed

    rheemed

    Member

    Joined:
    Jul 14, 2009
    Messages:
    5
    Likes Received:
    0
    when contactor manually pushed in, compressor seems to run OK, but contactor won't stay drawn-in, fan runs constantly
     
  4. Jul 14, 2009 #4

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    check the voltage AT the transformer. If you have 24VAC on the secondary side of the transformer then you might have a bad T-stat or a bad low voltage wire. If no 24VAC at the transformer, then you just got real luck, just make sure to replace w/like rated transformer.
    You may run into a universal transformer just be sure to wire it up for 120VAC on the primary side.
     
  5. Jul 14, 2009 #5

    rheemed

    rheemed

    rheemed

    Member

    Joined:
    Jul 14, 2009
    Messages:
    5
    Likes Received:
    0
    Thanks Kok328, I'm a semi-literate fool when it comes to AC/electrical, the only stuff I've learned is from trial&error and phone calls to friends of friends in the business

    is the transformer in the air handler(inside) or condenser(outside)?
     
  6. Jul 14, 2009 #6

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    Hey no problem, it's called learning. I didn't know any of this at a point in my life and never took any formal or informal training. It will be in the air handler end. The best way to find it, would to trace the low voltage wires usually, thin wires in a brown casing. Working backwards, they will go from the condensor unit to the T-stat and then terminate in the air handler at a terminal strip. This terminal strip is powered by the transformer. It's job is to reduce 120VAC to 24VAC. If it goes bad you won't be getting 24VAC anymore and of course if it is not getting 120VAC then you won't get 24VAC with means the problem is not the transformer but further upstream.
     
  7. Jul 14, 2009 #7

    rheemed

    rheemed

    rheemed

    Member

    Joined:
    Jul 14, 2009
    Messages:
    5
    Likes Received:
    0
    had an AC tech friend stop by, turned out to be delay relay on outside unit

    the old mercury switch therm required it

    with the new therm it's built in, so he bypassed the outside delay, done

    she's cooling down from 91 now, we'll see what happens when it gets to 74

    thanks a "ton" for replying kok328, I'll probably be back one day, hopefully for something different
     