    For a 2.0E LVL, proximately how much stronger is one 3 1/2" x 9 1/2" LVL vs two 1 3/4" x 9 1/2" bond together, assume the two LVL are binded accroding to the manufactory's guide ?

    I can get two 1 3/4" at HD for about $55 each. However, to order a 3 1/2", it cost $260 from a local lumber yard.
     
  2. Jan 24, 2012 #2

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,904
    Likes Received:
    3,122
    Each product and each manufacture has a different chart so the lumber yard should be able to check that for you.
     
  3. Jan 24, 2012 #3

    minimii

    minimii

    minimii

    Active Member

    Joined:
    Dec 5, 2011
    Messages:
    30
    Likes Received:
    0
    I have called GP and other manufactories, still did not get any response back yet.
    Does anybody know roughtly, (for a span of around 10ft), how much load does two 1 3/4" can provide, comparing one 3 1/2"? 90%, 80%?

     
  4. Jan 24, 2012 #4

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,904
    Likes Received:
    3,122
  5. Jan 24, 2012 #5

    BridgeMan

    BridgeMan

    BridgeMan

    Well-Known Member

    Joined:
    Aug 11, 2011
    Messages:
    744
    Likes Received:
    80
    As per the tables, they're identical--both in bending moment and shear strength. That being said, going with a single larger member would avoid any weakening caused by the fasteners used to attach the smaller units together. Shear resistance at the ends, in particular, could be compromised by too many through-bolts.
     
  6. Jan 25, 2012 #6

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,904
    Likes Received:
    3,122
    Engineers only ask for bolting when the beam is close to the upper limits. For most of your work they allow us to nail them together three 3" nails 12 to 16" on center.
     