Checking all my work before inspector is called in Michigan, can my ground and neutral connect in the same bus bar? New 100 amp box with two bus bars, both still connected, just wanna double check. Have whole house done, just checking. Also, do I have to staple wires to studs in wall, or just inder house along floor joists?
In the panel with the main disconnect you can put the grounds and neutrals in the same bus. One neutral per hole. If the walls are open then staple or support every 4 feet. If fishing cable through already finished walls then you do not need to bust open the walls to staple.
Thank you very much. I know that only one nuetral per hole (like you said), but what about adding a ground in the same hole with it?
Thank you both very much. I am currently fighting to keep working on the studded home that I bought for xmas. I just finished mudding the drywall, now I have to tear down one interior and one exterior wall for them to inspect it all. I am from a state and area where there are no codes, this code stuff is really irritating. I have ran everything correctly except I have to seperate the wires in the box now. Thank you so much, I rwally appreciate the help. Hopefully I will be able to continue with the restoratiom and move in soon.