We moved into a new home with a 200 amp main panel. The garage is detached behind the house about 30 feet and I need to run a 240 v high capacity line to a subpanel. The estimated max load will be total 80 amp serving up to a 50 amp level 2 charger plus shop tools: 220v 3hp is largest equipment and only one machine used at a time).
The total wire run from the main panel to the sub panel in the garage will be 50 ft or less. The feed from main to sub panel will be 3 conductors of 6 AWG THHN plus ground in 1" PVC conduit secured to the fence on the side of the yard. From main panel to beginning of PVC is metal conduit buried 6" under a crushed stone side walkway (about four feet total run). I know the subpanel will require a separate grounding rod to earth because of the separation from the main panel.
My question:
Is the 6 AWG overkill or suitable for this run? Other than having a certified electrician make the connection to the main panel and look over the general installation, do you have other opinions about this project? Is the 80 amp sub panel overkill?
The total wire run from the main panel to the sub panel in the garage will be 50 ft or less. The feed from main to sub panel will be 3 conductors of 6 AWG THHN plus ground in 1" PVC conduit secured to the fence on the side of the yard. From main panel to beginning of PVC is metal conduit buried 6" under a crushed stone side walkway (about four feet total run). I know the subpanel will require a separate grounding rod to earth because of the separation from the main panel.
My question:
Is the 6 AWG overkill or suitable for this run? Other than having a certified electrician make the connection to the main panel and look over the general installation, do you have other opinions about this project? Is the 80 amp sub panel overkill?