    I am adding a breaker for a 24000 BTU AC/heat pump. What size breaker would that be?
     
  2. May 3, 2010 #2

    Cork-Guy

    Cork-Guy

    Cork-Guy

    Cork Flooring Pros

    Joined:
    Oct 5, 2009
    Messages:
    243
    Likes Received:
    0
    The smartest choice would be what's recommended by the manufacture; which will be the "only" right answer.
     
  3. May 3, 2010 #3

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    Check the amperage rating on the nameplate of the unit your installing.
     
  4. May 3, 2010 #4

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    You also need a breaker the 'trip curve' of which handles compressor [motor] loads, otherwise you might need a 'soft start' kit.
     
  5. May 4, 2010 #5

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    On the side of every unit is a "Minimum circuit ampacity" and a "Maximum fuse or breaker size".

    You size the wire to the former and the breaker to the latter.

    DO NOT guess at this. BTU ratings are irrelevant.
     