So my buddy calls me over to his house. He abandoned his AC unit and wants to use the 220VAC 50A setup to run power to a Tesla charger. He ran the #6 wire in conduit for the 14-50 NEMA receptacle in the garage. BUT, when he got to the disconnect he could not figure what to do. The picture shows his problem ... The 14-50 receptacle needs two power legs plus a neutral and a ground. The service into his disconnect has two power legs and a neutral but no ground. I'm not sure what to tell him. What is the answer?
 

Attachments

Snoonyb

Well-Known Member
Joined
Sep 30, 2006
Messages
4,191
Reaction score
844
Welcome.

Purchase lengths of white and green conductor, some pull lube and use the existing white to pull the new conductors.

Stranded copper make neat crafts.
 

kok328

Well-Known Member
Joined
Nov 19, 2007
Messages
3,017
Reaction score
313
you didn't mention what diameter conduit is there. need to check conduit sizing chart to see what (4) #6 wires requires.
 

JoeD

Well-Known Member
Joined
Mar 15, 2006
Messages
1,731
Reaction score
341
Is the conduit metal? Is it continuous to the panel? If it is then the conduit is the ground.

Is that picture the AC box or the disconnect. It could also be that the AC does not need a neutral and there is not one in the AC box.
 

WasVilla

New Member
Joined
Oct 8, 2020
Messages
3
Reaction score
0
Location
San Diego
Answer was simple. Test box to see if grounded (yes). Add ground lug to box. Attach hot leads, neutral per normal. Connect green ground wire to ground lug. ALL GOOD.
 