I didn't realize we were talking about an electric heater with A/C.
That 60 amp breaker is not for the A/C.
Turn on power to the air handler and see if it is flashing diagnostics codes.
 

WyrTwister

Well-Known Member
Joined
May 26, 2014
Messages
326
Reaction score
60
One thing I noticed about the photo of the circuit breaker , the lugs where the 2 large black wires terminate , show corrosion .

With the circuit breaker in your panel turned on . Be CAREFUL !

If you have a volt meter & wearing leather or rubber gloves , test to see if you have 240 VAC at the 2 black wires / lugs

If good , test at the 2 lugs at the opposite end of the circuit breaker . Where the small black & small red wires are located .

God bless
Wyr
 
Last edited:

o2284200

Member
Joined
Oct 22, 2012
Messages
221
Reaction score
11
Just a hopeful shot in the dark.
Thanks!
Hoping someone more knowledgeable than I might be able to look further at the wiring diagram to see if there are provisions for a panel or door safety switch.
 

WyrTwister

Well-Known Member
Joined
May 26, 2014
Messages
326
Reaction score
60
Did not see a door switch in the wiring diagram .

Can not remember the correct name , but the diagram looks like this may be a variable speed motor ?

God bless
Wyr
 

o2284200

Member
Joined
Oct 22, 2012
Messages
221
Reaction score
11
Did not see a door switch in the wiring diagram .

Can not remember the correct name , but the diagram looks like this may be a variable speed motor ?

God bless
Wyr
Great, thanks!

If no door switch, we're back to:
Power on to air handler...
No flashing codes or lights.

FWIW, as for the motor, others have told me the following:
the unit has a X-13 constant torque motor which is tricky for some Pros and hard for a DIYer to troubleshoot... It uses a low voltage signal from the circuit board to energize the motor. Has no capacitor and is not a PSC motor. You need a flow chart and some electrical experience and test meter and to follow the chart steps to check it, not easy to do over the net.
Here's a pic of wiring diagram for ez viewing:
 

nealtw

Contractor retired
Joined
Nov 4, 2010
Messages
24,768
Reaction score
3,395
Location
Chiliwack BC Canada
this will help understand some of the wiring but right at the end he talks about a flood switch that turns everything off if the water isn't draining
[ame]https://www.youtube.com/watch?v=pCgPskm9aHs[/ame]
 

nealtw

Contractor retired
Joined
Nov 4, 2010
Messages
24,768
Reaction score
3,395
Location
Chiliwack BC Canada
Neal, where are we with this one?

What's not working and what has been tested?:confused:
Givin the location of the motor and individual plugs on it it will be hard to test for power there. So before he gets into that I just want to make sure it isn't some other switch like the float or something. But as usual, I am over my head.
We will need a better picture of the wiring diagram and maybe by feel he can find the other ends of the wires to test them.:hide:
 