Trane Heat Pump Assistance

Discussion in 'HVAC' started by outsideperson, Feb 16, 2009.

  1. Feb 16, 2009 #1

    outsideperson

    outsideperson

    outsideperson

    New Member

    Joined:
    Feb 16, 2009
    Messages:
    2
    Likes Received:
    0
    Despite my best effort to find a good installer, the installation of a new heat pump system has been a nightmare. Thankfully, with persistence, I have been able to get problems resolved.

    However, over the weekend, I realized that during the defrost cycle, the auxiliary heat does not kick in. I had 40 degree air coming out of the registers during the defrost cycle. Outside temperature was in the high 20s. When I put the system in emergency heat mode, I did get warm air from the registers. There must be a wiring problem. Before I call in the installer again, I would like to find out what is the correct wiring. I don’t plan to change any of the wiring myself, I just would like to know what is correct so I can make sure the job is done right.

    Below is the information on the equipment and how they are wired:

    Trane Heat Pump: 4TWX5024A1000A
    Air Handler: 4TEE3F1B1000A
    Thermostat: TCONT802AS32DAA
    10 KW back-up heat: WBAYHTR1410BRKR

    The wiring is as follows:

    Thermostat > Air Handler > Heat Pump

    Red > Red > Red
    Orange > Orange > Orange
    Blue > Blue > Blue
    Yellow > Yellow > Yellow
    Green > Green > Green (not wired – just hanging loose)
    W1 –white > W1 –white

    The dip switches on the air handler are set as follows for Comfort-R:

    1 off
    2 on
    3 off
    4 off
    5 on
    6 on
    7 on
    8 off

    The green wire to the heat pump is connected at the air handler, but just hanging down and not connected to anything at the heat pump.

    Also, my understanding was the auxiliary heat was to go on in two stages. Is the wiring setup to do this?

    Any help that can be provided will be gratefully appreciated. I just want the system to run correctly. Thanks.
     
  2. Feb 17, 2009 #2

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    Any jumper wires in the T-stat or terminal strip inside the unit itself?

    Green wire is for the indoor fan blower motor.
     
  3. Feb 17, 2009 #3

    outsideperson

    outsideperson

    outsideperson

    New Member

    Joined:
    Feb 16, 2009
    Messages:
    2
    Likes Received:
    0
    at the thermostat, the R and Rc have a jumper between them. There are no other jumpers at the thermostat, air handler or heat pump.
     
  4. Feb 17, 2009 #4

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    Unfortunately, I don't know much about heat pump control wiring but, it sounds like your missing a jumper wire somewhere.
     
  5. Feb 19, 2009 #5

    whyme

    whyme

    whyme

    Member

    Joined:
    Feb 18, 2009
    Messages:
    15
    Likes Received:
    0
    i almost went into hvac boy i'm sure glad i didnt, cold during the winter, hot durring the summer then its all back breaking labor , while you get nothing for PAY!!! gee sign me up!!!!!
     