Transformer not reading 24 volts

House Repair Talk

Help Support House Repair Talk:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

manofthehouse

New Member
Joined
Jun 4, 2020
Messages
1
Reaction score
0
Location
44260
So guys, I have 2 identical Bryant heat pump units. Unit # is running normally and unit #2 is down. Blower fan and capacitor is working normally on unit #2. I test the transformer and it read 120 volts at the primary but zero volts at the secondary. The transformer has some continuity. So what I did was removed the transformer from unit #2 to unit #1 and moved the one from unit#1 to unit#2. I noticed that both of the transformers read 24 volts at the secondary on unit #1. When I put both on unit #2 no voltage is read at the secondary. I has being working on couple of days now and I can't figure it out what is the problems. Any ideas what is to be the problems here.
 

Attachments

  • 20200529_125158.jpg
    20200529_125158.jpg
    65.8 KB · Views: 3
  • 20200529_124431.jpg
    20200529_124431.jpg
    60.3 KB · Views: 3
Could you be reading back feed voltage on unit #2 primary?
 