Working on a 240v (15A) circuit. Black to neutral = 121v, Red to neutral = 122v, Black to Red = 4.5v??? What am I missing - is this right? Why?
One of the hot leads is dead. The breaker is installed wrong and both hots are on the same leg of the service. You used a tandem breaker instead of a two pole breaker. Is this a new install or has it been working before?
Are you taking these reading from the breaker or from the end of the wires?
Is your meter on the correct setting for measuring 240V ?
and set your meter above 200v, your measuring 240vI would also check voltages at the breakers.
and set your meter above 200v, your measuring 240v
I would also check voltages at the breakers.
Hamberg: Yes as advised take your readings at the breaker itself first. Start at the beginning first.
If the readings are correct at the breaker then go to the next point of connection and take your readings there.
If one stat died and you are taking readings after that stat this may be the reasoning of no 240v. I'm wondering why a neutral is in play though. I am not that familiar with floor heating so maybe it is a 120/240v circuit.
yes and you indicated that you meter is set for 200V range, so your meter can not measure between black and red. set the meter higher and recheck the breaker.each pole is only 120v, right?
There is no neutral in this setup..
Hamberg: Yes as advised take your readings at the breaker itself first. Start at the beginning first.
If the readings are correct at the breaker then go to the next point of connection and take your readings there.
If one stat died and you are taking readings after that stat this may be the reasoning of no 240v. I'm wondering why a neutral is in play though. I am not that familiar with floor heating so maybe it is a 120/240v circuit.
.
yes and you indicated that you meter is set for 200V range, so your meter can not measure between black and red. set the meter higher and recheck the breaker.
There is no neutral in this setup.
There is no neutral in this setup.
check all you want. until the MM is set correctly you won't get 240V of any 2 pole breaker.You should have 240v at the breaker. If you only have 4.6v I would check another 240v breaker just for a sanity check. If one side of the breaker is faulty the voltage could just be thermostat feedback. BTW is the other mat heating properly as you troubleshoot this thermostat?