Water leaking from front of window a/c.

Discussion in 'General Appliance Discussion' started by farmerjohn1324, Oct 3, 2017.

Help Support House Repair Talk by donating:

  1. Oct 3, 2017 #1

    farmerjohn1324

    farmerjohn1324

    farmerjohn1324

    Well-Known Member

    Joined:
    Aug 5, 2016
    Messages:
    963
    Likes Received:
    103
    Got a message from a tenant saying this.

    She leaks it doesn't seem to be dripping from the back.

    I'm going there tomorrow. My plan is to take it out of the wall, clean the filter, take the casing off, clean all the nasty stuff from the inside of the pan, and drill a hole in the back to allow for better drainage, making sure to avoid copper pipes.
     
  2. Oct 3, 2017 #2

    frodo

    frodo

    frodo

    Senior Member

    Joined:
    Aug 5, 2008
    Messages:
    3,066
    Likes Received:
    1,196
    if the unit does not tilt a little out the window it will leak

    also, if the unit is low on freon, the coil will freeze and drip out the front
     
  3. Oct 3, 2017 #3

    farmerjohn1324

    farmerjohn1324

    farmerjohn1324

    Well-Known Member

    Joined:
    Aug 5, 2016
    Messages:
    963
    Likes Received:
    103
    Yes, I didn't mention the tilt. I thought that was too obvious. It has been in that window for years so I didn't think that was the problem.

    How do I test if it's low on freon? And is this something I can remedy myself?
     
  4. Oct 3, 2017 #4

    frodo

    frodo

    frodo

    Senior Member

    Joined:
    Aug 5, 2008
    Messages:
    3,066
    Likes Received:
    1,196
    no, i do not think you can do it yourself
     
  5. Oct 3, 2017 #5

    woodchuck

    woodchuck

    woodchuck

    Well-Known Member

    Joined:
    Jul 19, 2008
    Messages:
    272
    Likes Received:
    28
    The moisture in the air condenses on the coil and will frost up a little and melt off. This is where the water comes from. If its low on freon it keeps building up eventually blocking the coil preventing the air from circulating.. When you first turn it on you can take the filter off and observe the coil frost up and defrost. Some units are supposed to be drip free and don't have a drip hole. The water is supposed to be evaporated by the condenser fan blowing across it.
     
    Connie B likes this.
  6. Jun 8, 2018 #6

    Dennis Palmer

    Dennis Palmer

    Dennis Palmer

    Member

    Joined:
    May 29, 2018
    Messages:
    13
    Likes Received:
    0
    Normally water leakage problem occurs in window AC when the air filter is dirty, faulty, partially or completely clogged. To overcome this problem, you should clean or change your air filter and check AC refrigerant levels regularly etc.
     
  7. Jun 8, 2018 #7

    Darren Kent

    Darren Kent

    Darren Kent

    Member

    Joined:
    Jun 8, 2018
    Messages:
    6
    Likes Received:
    1
    Location:
    Ohio
    Water leakages occurs from the dirty drain holes of AC. To prevent this clean the drain holes regularly. This may reduce the chances of big problem in future.
     
  8. Jun 8, 2018 #8

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,853
    Likes Received:
    280
    before you start drilling holes, verify this is not a "Sling Fan" model.
     
    Connie B likes this.
  9. Jun 9, 2018 #9

    BuzzLOL

    BuzzLOL

    BuzzLOL

    Member

    Joined:
    Oct 27, 2015
    Messages:
    13
    Likes Received:
    3
    Yes, if the tilt is right, prolly just needs cleaning... a certain level of water inside helps it cool more efficiently... the hot side of the compressor tubing usually runs through the condensate water and the water cools it very quickly and, also, the heat causes the water to evaporate quicker, as well...
     
  10. Jun 25, 2018 #10

    8307c4

    8307c4

    8307c4

    Member

    Joined:
    Nov 6, 2007
    Messages:
    13
    Likes Received:
    5
    Mine was doing something similar, except instead of dripping inside it was slinging condensate out the top fins by picking up water from the bottom "pan" with the fan blades. I didn't think it was low on freon because the evap coils would've frozen to a solid block of ice and then nothing would drip, as well the unit wouldn't cool if this were the case.
    I did look inside but it wasn't too dirty, really wasn't hardly any dirt at all.
    The pan however was full of water, I could see it, I could also see how the fan was just slicing and dicing through the water with every revolution...
    Drilling that little hole solved the problem for me, I used a 1/4" drill bit to make sure it was just big enough so no little piece of dirt would clog it up.

    I was amazed there was no hole for the condensate to drain at all...
    I did remember it being that way the day I bought it but I didn't think much of it at the time, figured it was intentionally that way by design... Is this how they make these units now? You have to drill the little drain hole yourself?
    Still not sure what to think, but it works great now.
     